Ask Your Question
0

How to trip one winding in a 3-winding transformer?

asked 2015-10-09 14:19:30 -0600

lhmus gravatar image

updated 2015-10-15 08:43:55 -0600

Hello,

I can trip one winding for a 3-winding transformer in PSS/E. I checked the API manual. THREEWNDIMPEDCHNG3 has a parameter, intergar8, for resetting the transformer status but only 0 and 1 for out-service and in-service options. Is it possible just to trip one winding for a 3-winding transformer?

Thanks!

edit retag flag offensive close merge delete

3 answers

Sort by ยป oldest newest most voted
0

answered 2016-09-19 08:20:52 -0600

perolofl gravatar image

The API manual is not complete. Parameter INTGAR(8) can be set to openan individual winding: 0 = out of service, 1 = in service at all windings, 2 = winding 2 is open, 3 = winding 3 is open, 4 = winding 1 is open.

edit flag offensive delete link more

Comments

Correct!!!

lhmus gravatar imagelhmus ( 2016-10-03 10:00:00 -0600 )edit
1

answered 2015-10-16 12:43:57 -0600

jconto gravatar image

You can 'open' a single winding of a three-winding transformer by:

  1. Insert a zero-impedance line between each winding and the network bus.
  2. solve the load flow
  3. now, open one of the zero-impedance to simulate the 'single winding opening' condition.
  4. solve again, and continue with your analysis.
edit flag offensive delete link more
0

answered 2015-10-23 10:42:16 -0600

lhmus gravatar image

updated 2015-10-23 10:44:03 -0600

Thank jconto! Need to replace the three buses on the 3-winding xfmr with three new buses, then connect them to their network bus with a ZBR. That is what I do. Any other method for sharing?

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2015-10-09 14:19:30 -0600

Seen: 8,644 times

Last updated: Sep 19 '16