0

Can't find exdc1 model in PSS/E 33

I have an IEEE 39 bus model, and I am trying to convert dynamic file .dyd from PSLF to PSS/E .dyr Following the suggestion of https://psspy.org/psse-help-forum/question/1001/dyr-file/, I compared the syntax in both, and found EXDC1 is in PSLF, but not in PSS/E 33. The EXDC2 in PSS/E 33 is quite similar to EXDC1 in PSLF. I was wondering if EXDC1 is called differently or it doesn't exit in PSS/E 33?

SC's avatar
30
SC
asked 2014-03-04 09:20:32 -0500, updated 2014-03-04 09:31:47 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

The EXDC1 (rotating DC machine exciter model) in PSLF is the same as the IEEEX1 in PSS/E. Both of them are derived from IEEE standard DC1A model.

yfwing's avatar
436
yfwing
answered 2014-03-04 11:14:59 -0500
edit flag offensive 0 remove flag delete link

Comments

@yfwing, it's good to know that. Thank you.

SC's avatar SC (2014-03-04 12:14:11 -0500) edit
add a comment see more comments