Are there any settings in PSS®E v36 to automate OLTC operation?

asked 2026-05-24 09:03:37 -0500

Raushan gravatar image

Are there any settings in PSS®E v36 to automate OLTC operation? Specifically, I want to understand how the tap position of one transformer can be automatically adjusted to control the voltage at another bus.

edit retag flag offensive close merge delete

1 answer

Sort by » oldest newest most voted
1

answered 2026-05-25 05:32:03 -0500

perolofl gravatar image

In transformer control data:

  • Enter the bus number in field "Controlled Bus Number"
  • Select Control Mode "1-Voltage"
  • Select "Auto Adjust"
  • If controlled bus is not From or To bus number, select proper setting in check box "Controlled Bus On Winding 1 Side"