Are there any settings in PSS®E v36 to automate OLTC operation?

  • retag add tags

Are there any settings in PSS®E v36 to automate OLTC operation? Specifically, I want to understand how the tap position of one transformer can be automatically adjusted to control the voltage at another bus.

Raushan's avatar
11
Raushan
asked 2026-05-24 09:03:37 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

In transformer control data:

  • Enter the bus number in field "Controlled Bus Number"
  • Select Control Mode "1-Voltage"
  • Select "Auto Adjust"
  • If controlled bus is not From or To bus number, select proper setting in check box "Controlled Bus On Winding 1 Side"
perolofl's avatar
3.8k
perolofl
answered 2026-05-25 05:32:03 -0500