Tap Changer Vs Regulation Control

asked 2025-09-04 06:10:56 -0500

_____ja gravatar image

updated 2025-09-09 06:25:23 -0500

perolofl gravatar image

Question for practitioners:

Can I model this in PSS/E?

A) Tap Changer located on High side and Regulation Control on High Side Bus

B) Tap Changer located on High side and Regulation Control on Low Side Bus

C) Tap Changer located on Low side and Regulation Control on High Side Bus

D Tap Changer located Low side and Regulation Control on Low Side Bus

What will be different in PSS/E configuration? Can you provide example screens?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2025-09-09 06:41:41 -0500

perolofl gravatar image

Of course!

Tap changer side:

In the Transformer Data Record the checkbox "Winding 1 on From end" decides the location of the tap changer. The tap changer is always on Winding 1 side. If the tap changer is at From bus side, the check box shall be enabled.

Controlled bus:

The controlled bus i defined in "Controlled Bus Number".

In the example below the tap changer is on high tension side and the voltage control on low the low tension side of the transformer.