0

How to get the values for SCR and X/R ratio using PSS/E?

  • retag add tags

I want to calculate the SCR and X/R at POC using PSS/E. I know there is automatic sequencing fault calculation and IEC60909 fault calculation function and in pss/e but I never used it. so, please teach me how to use and to get those values?

anonymous user
asked 2025-08-28 19:08:27 -0500, updated 2025-08-28 19:34:32 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

Use Short Circuit - ASCC and select output "total fault currents with Thevenin Impedance".

perolofl's avatar
3.8k
perolofl
answered 2025-08-29 08:38:59 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments

Your Answer