0

Initial Conditions for Ef and If

Dear members, I need to match the measurements to verify the exciter. How do you set the initial conditions like Ef and IF? Any reference to calculate the machine initial conditions?

kuchow's avatar
1
kuchow
asked 2025-08-26 20:39:05 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

Dear Kuchow, In dynamic simulations, the exciter voltage and current is usually calculated based on the load flow conditions and can be accessed by the array table EFD(I), where I is the machine index. I hope this helps, BR

cBal's avatar
1
cBal
answered 2025-08-27 06:11:59 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

1- Initialise simulation and check the EFD for the generator (printed in progress window).

2- Reload the case and update Vsched or change Qmax & Qmin to enforce another Qgen.

3- Convert and initialise again.

4 - Repeat 2 & 3 until Efd is matching the measurement.

perolofl's avatar
3.8k
perolofl
answered 2025-08-27 08:30:52 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments

Your Answer