SCR and X/R ratio of PLBVFU1 model

  • retag add tags

I read a post titled 'How to calculate SCR, X/R ratio in PSS/E?' and tried to simulate the LVRT test of a wind farm.

However, when i try to play back voltage of 0pu, the voltage at the POM stays around 0.3pu due to the ZSORCE of the infinite bus generator.

Is there a way to simulate PLBVFU1 model using specified SCR and X/R ratio values?

anonymous user
asked 2025-06-24 22:26:04 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Skip the SCR and use an infinite generator instead. Increase Mbase and decrease zsorce.

perolofl's avatar perolofl (2025-06-25 03:49:25 -0500) edit
add a comment see more comments

1 Answer

0

When using PLBVFU1, intention is to apply the required playback at the POC. Use an infinite generator with a very low impedance SCR(9999) branch to play the same voltage and frequency at the POC. Also the Playback generator is a voltage source behind an impedance. To get the same voltage at the terminal make your infinite machine MVA higher or reduce machine impedance (specifically X).