CBEST model for BESS

asked Feb 11 '5

sakunrasilka gravatar image

updated Feb 11 '5

perolofl gravatar image

I am an undergraduate doing a research project on BESS. i used a generator as a conventional machine and used the cbest model with below parameters,

1       PMAX (pu on MBASE)
1.1     OutEff (>= 1) Output Efficiency                                 
0.9     InpEff (<= 1) Input Efficiency                                                                  
1.2     IACMAX (pu)
100     KAVR, AVR gain
0       T1, AVR time constant (sec)
1       T2, AVR time constant (sec)
0.05    T3, AVR time constant (sec) ( >0 )
10      T4, AVR time constant (sec)
1       VMAX, AVR speed limit (pu)
-1      VMIN, AVR speed limit (pu) ( <0 )
0.025   DROOP (pu)

Is it enough to model the bess or do i need to select a model for exciter, governor, stabilizer,..

1 answer

Sort by » oldest newest most voted
0

answered Feb 11 '5

perolofl gravatar image

No other model is needed. The only possible auxiliary models are a stabiliser which will modulate VOTHSG or a compensator model to change the measured voltage.

The active power output is changed manually in the simulation with VAR(L).

link

Comments

Thank you for replying. I'm targeting to achieve frequency regulation with a BESS. Is the cbest model is the only model which i can use for BESS or are there other models too.

sakunrasilka gravatar imagesakunrasilka (Feb 11 '5)