The impact of BESS on power system stability
Hello everyone, I am researching the impact of BESS on power system stability. In the simulation, a three-phase short-circuit fault occurs at the 50% position of the transmission line for 0.1s before being cleared. During the fault, the frequency and voltage response are quite irregular compared to the case without BESS. Below are the dynamic parameters of the BESS I used. Where is this parameter set incorrect? P/s: I can't upload directly file to here, so this is link folder .dyr and .out file. Thank you
link folder .dyr and .out file
/ BESS
1 'USRMDL' '1' 'REGCAU1' 101 1 1 14 3 4 0
@! Tg Rrpwr Brkpt Zerox Lvpl1
0.017 180.0 15 0.05 1.22
@! Volim Lvpnt1 Lvpnt0 Iolim Tfltr Khv Iqrmax Iqrmin Accel
1.8 0.2 0.05 -0.8 0.02 0.1 999 -999 0.7 /
1 'USRMDL' '1' 'REECAU1' 102 0 6 45 6 9 0 0 0 0 0 0
@! Vmax Vmin Tfltr dbd1 dbd2 Kqv
1.2 0.8 0.02 -0.05 0.05 1.0
@! QMax QMin Kqp Kqi Kvp Kvi Tiq
1 -1 1 1 0 1 0.02
@! Pmax Pmin Vmax Vmin Kvp Kvi Tpord
1.0 -1.0 1.2 0.8 0 1 0 1 0 0.02
@! dPmax dPmin PMAX PMIN Imax Tpord
1.0 -1.0 1 -1.0 1.2 0.02
@! Vq1 Iq1 Vq2 Iq2 Vq3 Iq3 Vq4 Iq4 Vp1 Ip1 Vp2 Ip2 Vp3 Ip3 Vp4 Ip4
0 0.5 0.2 0.5 0.4 0.5 1.1 0.5 0 1 0.5 1 0.9 1 1.1 1 /
1 'USRMDL' '1' 'REPCAU1' 107 0 7 27 7 9
@! Rmt Bi Bj id droopflg VQflag Fflag
8 12 8 '1' 1 1 1
@! Tfltr Kp Ki Tft Tfv Vfrz Rc Xc Kc emax emin
0.02 12.5 0.05 0.01 0.05 0.5 0 0 0.04 0.1 -0.1
@! dbd1 dbd2 Qmax Qmin Kpg Kig Tp
0 0 0.99 -0.99 1 0.01 0.01
@! fdbd1 fdbd2 femax femin Pmax Pmin Tg Ddn Dup
-0.0001 0.0001 99 -99 1 -1 0.1 110 110 /