power flow result question

asked 2025-01-03 15:04:07 -0600

anonymous user

Anonymous

Hi, I m running a very simple test case with 1 generator (swing bus) and a stepped load totaling up to the the real and reactive power capability of the generator (3MW and 1,4MVARs), there is no source of losses (ideal line, no xfrm...) but the load flow show Pgen 32MW. not sure where the power is going...

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2025-01-04 05:37:02 -0600

chandv gravatar image

Successful convergence of solution will always be balanced in generation, losses and load terms. Though difficult to comment without details, this can be due to some modeling issue. Pl. check line flows from both end. Wrong parameters may consume MW and MVAR. If possible, share more detail to enable us supporting on this matter.