First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question
2

Definition of phase shifter transformer

asked Sep 29 '4

Yoyo gravatar image

updated Sep 29 '4

Hello everyone!

Can someone explain or exchange a picture for me from the psse window of a correctly configured transformer for a phase shifter transformer? I found an explanation on the website, but it was not very detailed. I understand that it is necessary to define code number 3 in the control, as well as to define a desired range of angles (R1min, R1max), number of Taps. What else is required? I fill these things but there seems to be no change in the situation and the current supply in the transformer in different scenarios. Unfortunately I cannot attach a picture. If any of you can upload a picture with an explanation, I would be very happy! Thank you for your help

Comments

Thank you very much. The tutorial was very helpful!

Yoyo gravatar imageYoyo (Sep 30 '4)

1 answer

Sort by » oldest newest most voted
2

answered Sep 29 '4

perolofl gravatar image

Also power limits must be given in Vmax, Vmin, see for example transformer 202 - 203 in savnw network in Example folder:

image description

When solving the load flow option "Adjust phase shift" must be selected:

image description

link