Ask Your Question
0

Definition of phase shifter transformer

asked 2024-09-29 02:33:08 -0500

Yoyo gravatar image

updated 2024-09-29 02:54:47 -0500

Hello everyone!

Can someone explain or exchange a picture for me from the psse window of a correctly configured transformer for a phase shifter transformer? I found an explanation on the website, but it was not very detailed. I understand that it is necessary to define code number 3 in the control, as well as to define a desired range of angles (R1min, R1max), number of Taps. What else is required? I fill these things but there seems to be no change in the situation and the current supply in the transformer in different scenarios. Unfortunately I cannot attach a picture. If any of you can upload a picture with an explanation, I would be very happy! Thank you for your help

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2024-09-29 07:07:58 -0500

perolofl gravatar image

Also power limits must be given in Vmax, Vmin, see for example transformer 202 - 203 in savnw network in Example folder:

image description

When solving the load flow option "Adjust phase shift" must be selected:

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2024-09-29 02:33:08 -0500

Seen: 14 times

Last updated: 13 hours ago