No active table model for generator 1 at bus 1119 [xxxx PH 132.00] -- RUN will not be accessible

asked 2024-09-27 07:04:19 -0500

junaid2657@gmail.com gravatar image

While initializing dynamic simulation, I getting this message in the progress window on multiple generators. Can anyone help me out?

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
1

answered 2024-09-27 08:14:40 -0500

perolofl gravatar image

You need a dynamic generator model for all in-service generators in load flow.

Either add a generator model for each machine or GNET those generators, i.e. replace them with negative loads. In the latter case the dynamic behaviour of the generator will be ignored.

edit flag offensive delete link more
0

answered 2024-10-03 17:20:00 -0500

In addition to perolofl's answer, another reason to get the

"No active table model for generator ... at bus ...[..... 132.00] -- RUN will not be accessible"

is when the DYR models for these generators have mistakes that prevented PSSE from loading them successfully

edit flag offensive delete link more

Comments

I have received the DYR model from the consultant, they are already working on the same DYR models then why am I getting all these errors?

junaid2657@gmail.com gravatar imagejunaid2657@gmail.com ( 2024-10-04 09:10:45 -0500 )edit
<@junaid2657@gmail.com">p>@junaid2657@gmail.com I am not sure why would that be the case. Two things you can check: 1-Making sure you have the correct termination symbols at the end of the DYR 2-Try and load the DYR into PSSE manually and see what errors occur

Mohamed_M gravatar imageMohamed_M ( 2024-10-07 17:41:24 -0500 )edit

Appreciated, as I am new to dynamic simulation can you please elaborate how can I add DYR into PSSE manually? It might would be helpful to me. Thank you.

junaid2657@gmail.com gravatar imagejunaid2657@gmail.com ( 2024-10-07 21:25:01 -0500 )edit

You can do the following: 1-Open the .CNV case in PSSE 2-Go to File->Open. Then open the DYR file 3-Go to the Dynamics Data tab and see if the models are loaded correctly to the generator rows 4-Check the Output Bar in PSSE and look for any errors if step3 showed missing generator models

Mohamed_M gravatar imageMohamed_M ( 2024-10-08 17:21:02 -0500 )edit