No active table model for generator 1 at bus 1119 [xxxx PH 132.00] -- RUN will not be accessible
While initializing dynamic simulation, I getting this message in the progress window on multiple generators. Can anyone help me out?
add a comment
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
While initializing dynamic simulation, I getting this message in the progress window on multiple generators. Can anyone help me out?
You need a dynamic generator model for all in-service generators in load flow.
Either add a generator model for each machine or GNET those generators, i.e. replace them with negative loads. In the latter case the dynamic behaviour of the generator will be ignored.