No active table model for generator 1 at bus 1119 [xxxx PH 132.00] -- RUN will not be accessible

asked 2024-09-27 07:04:19 -0500

junaid2657@gmail.com gravatar image

While initializing dynamic simulation, I getting this message in the progress window on multiple generators. Can anyone help me out?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2024-09-27 08:14:40 -0500

perolofl gravatar image

You need a dynamic generator model for all in-service generators in load flow.

Either add a generator model for each machine or GNET those generators, i.e. replace them with negative loads. In the latter case the dynamic behaviour of the generator will be ignored.