Ask Your Question
1

Why to give a large MVA to this infinite machine and set its Xs = 0.01 or less when representing an SMIB ?

asked 2024-02-20 20:20:29 -0600

gabriel_ipu gravatar image

I'm trying to compare dynamics results with other software, and it only matches when i do this, why i would give a large MVA to an infinite machine ?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
1

answered 2024-02-21 11:15:56 -0600

perolofl gravatar image

The short circuit power from a generator can be estimated to Mbase/Zsorce. Hence, a large Mbase and small Xsorce will lead to a very high short circuit power contribution to the bus, i.e. an infinite bus!

For example, Mbase=10 000 MVA, Xsorce=0.01 --> Short circuit power = 10 000/0.01 = 1 000 000 MVA.

edit flag offensive delete link more