Dynamic simulation
How to use PSS/E to run a dynamic simulation of a single-phase short-circuit which, after a certain time, becomes a two-phase short-circuit on the same bus?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
How to use PSS/E to run a dynamic simulation of a single-phase short-circuit which, after a certain time, becomes a two-phase short-circuit on the same bus?
Unbalanced faults can be simulated if sequence data (zero and negative sequence) are present in the saved case.
Initialise simulation
Run to time t1
Apply unbalanced bus fault and select "Line-to-ground" fault
Run to time t2
Clear fault
Apply unbalanced bus fault and select
"Line-to-line or
Line-to-line-to-ground" fault
Clear fault
Run to t4
Thank you for your answer. But, how can we fix the impedances R L-L and X L-L or R L-G and X L-G of the faults?
For solid fault, use R L-L and X L-L = 0. For LLG fault set R L-G and X L-G = 0. For LL fault set X L-G = 9999.
Thank you for your answer