GGOV1 INITIALIZED OUT OF LIMITS
What can i do resolve this out of limits initialization?
GGOV1 AT BUS ### MACHINE 1 INITIALIZED OUT OF LIMITS
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
What can i do resolve this out of limits initialization?
GGOV1 AT BUS ### MACHINE 1 INITIALIZED OUT OF LIMITS
This means that Pgen in load flow is larger than or lesser than the Vmax/Vmin limits in the governor model.
Change Pgen in load flow or update the limits in GGOV1.