Ask Your Question
0

Low voltage crossing fault excised the REECA1 model

asked 2023-08-30 19:39:02 -0600

David___ gravatar image

updated 2023-09-05 02:24:52 -0600

When the voltage drop amplitude is less than 0.9pu and the failure time lasts for 2s, the REECA1 model is removed (the in service button is automatically unchecked), and a circuit breaker is displayed at the output bar. However, I have not set any protection device in the network, may I ask if psse has its own protection device? If I want to modify it, where should I modify it? Looking forward to your reply, thank you very much!

edit retag flag offensive close merge delete

Comments

Is model REECA1 disabled automatically during the simulation? Please explain further: "a circuit breaker is displayed at the output bar".

perolofl gravatar imageperolofl ( 2023-09-01 02:45:54 -0600 )edit

When the voltage is lower than 0.9pu and the failure time lasts for 2s, the output bar displays: 'Breaker timer started at TIME =12.000 for Generator"1 "connected at bus 1[535.008]' (Fault occurs at 10s)

David___ gravatar imageDavid___ ( 2023-09-01 03:58:04 -0600 )edit

Look at the output of the curve and see that the output of REECA1 becomes 0, then go back to the sld file and see that the REECA1 model becomes a dashed line.

David___ gravatar imageDavid___ ( 2023-09-01 03:58:16 -0600 )edit

Do you mean that generator 1 at bus 1 is tripped?

perolofl gravatar imageperolofl ( 2023-09-01 08:32:42 -0600 )edit

Yes,at 12s, the generator 1 at bus 1 is tripped

David___ gravatar imageDavid___ ( 2023-09-01 08:45:03 -0600 )edit

1 answer

Sort by » oldest newest most voted
0

answered 2023-09-05 02:42:53 -0600

perolofl gravatar image

There is a call of miscellaneous model VTGTPAT in the snapshot. This is an under/over voltage generator bus disconnection relay.

See spreadsheet: Dynamics data - Other Models - Miscellaneous.

edit flag offensive delete link more

Comments

I see it!Thank you very much for your answer!

David___ gravatar imageDavid___ ( 2023-09-05 02:51:19 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2023-08-30 19:39:02 -0600

Seen: 1,000 times

Last updated: Sep 05 '23