Initial conditions suspects in CMLDBLU2

asked Jun 13 '3

Erandika gravatar image

Hello everyone, I'm having trouble in figuring out the cause for the following initial conditions suspect.

 INITIAL CONDITIONS SUSPECT:
 I   DSTATE(I)    STATE(I)     MODEL             STATE     BUS#-SCT X-- NAME --X BASKV  ID
  83630   0.69850E-04 -0.68402E-02 CMLDBLU2           K+1     10000     Load 1   12.500  1
  83632   0.59582E-04  0.17921E-02 CMLDBLU2           K+3     10000     Load 1   12.500  1

I want to figure out if this happens due to a model error or due to a voltage issue. Thank You

1 answer

Sort by » oldest newest most voted
0

answered Jun 15 '3

jconto gravatar image

In theory, the DSTATE value should be zero, but in practice, a very small value is workable. I supplement the "initial conditions suspect" table listing with the plotting/evaluation of channels (Pe,Qe,..) after a dynamic simulation under no disturbance for the period of interest (a flatstart for 10 sec.?) An acceptable response would be a flat line with max. deviations smaller than 10e-2. Use PSSPLT to evaluate max. deviations. If the plot has larger deviations or oscillations, model parameters need adjustments.