Ask Your Question
0

Synchronous machines trip due to underspeed and overspeed

asked 2023-05-18 20:14:38 -0500

MuhammadH gravatar image

Hi, I am running a fairly large system and observing that during 3 phase fault, a few synchronous machines trip due to underspeed and overspeed. Even though, 1. The tripped generators do not have relays. 2. DYR-file has no call of 'NRCGP3U'. [Checked also spreadsheet Dynamics Data - Protection Models - Machine for any tripping models.] 3. Dynamic Simulation Option of 'Scan generators exceeding speed deviation threshold is disabled. [ierr = psspy.set_genspdev(0, 10, 0, 0) #status, speed, trip, icode]

Can you please help me understand the reason of the trip?

The simulation progress files show messages like below. * MACHINE 1 AT BUS 400 TRIPPED BY UNDERSPEED RELAY AT TIME = 5.2125 SECS. * MACHINE 1 AT BUS 300 TRIPPED BY OVERSPEED RELAY AT TIME = 5.0750 SECS.

Best Regards,

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2023-05-19 09:20:48 -0500

jconto gravatar image

Check that the dyr file does not contains double entries of models for those machines. Are machines 400-1 and 300-1 using user defined models? Sometimes such models contains speed relays.

edit flag offensive delete link more

Comments

Thanks for the response and suggestions, jconto. (1) I have checked the dyr, the units have been entered just once. (2) The units have been defined by GENTPJ1 (generator), ESST4B (exciter), HYGOVDU (turbine governor), and COMP (compensator). I do not see any relay model.

MuhammadH gravatar imageMuhammadH ( 2023-05-19 15:00:45 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2023-05-18 20:14:38 -0500

Seen: 323 times

Last updated: May 19 '23