In addition to what Berwin said, you can use the fact that v34 will still read a v33 idv to convert from v33 to v34 of the idv if that's what you want to do. To demonstrate this, I used v33 to record in an IDV a change to a bus voltage monitored limit. PSSE v33 recorded the change using "BATBUSCHNG3". I then opened v34, opened the same case, then started an IDV recording. I then ran the v33 IDV and stopped the IDV recording. The resulting IDV is the bus change command in v34, "BATBUSCHNG4".

Hope this helps,

Jeff Eggebraaten