First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
1 | initial version |
Check my post at "Solar PV using REGCA models" for a demo set that includes a flat start process. Study the base case and the commands used during the flat process.
Many flat start issues can be eliminated with a good base case. The base case should converged, network operating conditions be within limits (V of buses, P&Q output from generators, etc.). Next the load is converted using the activity CONL. Generation is converted, etc.
The flat start run can be stop just after the converted case and snap file are loaded/created. Check the dynamic table for models in yellow, that indicates some model parameters could be off from what PSSe expects. Correct the data at the dyre file and run again.
Also examine the log file, just around the STRT command, looking for suspect conditions warning/errors that would give a hint on the dynamic model producing the error.