  1. Calculate the three phase short circuit power at bus 4 with ASCC.

  2. Simulate a bus fault and use the following fault admittance in MVA: B = dV * Sc.

If the short circuit power is 5000 MVA and the voltage drop is 0.3 pu (1pu-0.7pu) the fault admittance becomes 0.3 * 5000 = 1500 MVA. The following fault is applied:

image description

This will roughly result in the wanted voltage dip to 0.7 pu. If needed, you can fine tune the fault admittance in order to come closer to 0.7 pu voltage.