In my experience (in the USA) the typical model we use for loads which can simulate FIDVR is the CMLDxx composite load model family. If you are dead-set on ACMTBL then I won't be able to help, but if you can use the CMLD model, then I can provide some typical parameters. See the model following my post.
You'll need to update the bus number and load ID. You can adjust the fractions of each motor type at CONS J+18 through J+22. The Motor D stalling parameters begin at CON J+103.
There is an absolute ton of material out there on these CMLD models, and I highly recommend reading some of it to ensure you are using the model as intended.
<bus number> 'USRLOD' <load ID> 'CMLDBLU1' 12 1 0 132 27 146 48
-1.0000 0.0000 0.40000E-01 0.40000E-01 0.75000
0.80000E-01 1.0000 1.0000 1.0000 0.90000
1.1000 0.62500E-02 1.0250 1.0400 30.000
5.0000 0.0000 0.0000 0.64000E-01 0.94000E-01
0.50000E-01 0.23300 0.18800 1.0000 0.70000
0.50000 -1.0000 2.0000 0.19200 1.0000
0.80800 0.0000 2.0000 -0.50001 1.0000
1.5000 -1.0000
3.0000 0.75000 0.40000E-01 1.8000 0.12000
0.10400 0.95000E-01 0.21000E-02 0.10000 0.0000
0.70000 0.20000E-01 0.20000 1.0000 99999.
0.50000 0.20000E-01 0.70000 0.70000 0.10000
3.0000 0.75000 0.30000E-01 1.8000 0.19000
0.14000 0.20000 0.26000E-02 0.50000 2.0000
0.60000 0.20000E-01 0.20000 0.75000 0.50000E-01
0.50000 0.20000E-01 0.30000 0.65000 0.50000E-01
3.0000 0.75000 0.30000E-01 1.8000 0.19000
0.14000 0.20000 0.26000E-02 0.10000 2.0000
0.65000 0.20000E-01 0.20000 1.0000 9999.0
0.50000 0.20000E-01 0.30000 0.65000 0.10000
9999.0 0.30000 0.20000E-01 0.50000E-01
1.0000 0.98000 0.60000 0.10000
0.10000 0.0000 0.0000 1.0000
6.0000 2.0000 12.000 3.2000
11.000 2.5000 0.86000 0.20000
0.95000 1.0000 -3.3000 0.50000
0.40000 0.60000 0.50000 15.000
0.70000 1.9000 0.10000 0.60000
0.20000E-01 1.0000 9999.0 /