The maximum ramp rate is set by parameter Uo (open) and Uc (close) in model WSIEG1.

In model GGOV1 the maximum ramp rate is set by parameter Ropen and Rclose.

I don't understand the second question. The secondary control with gain Kimw will override the droop contol and bring the generator electric power back to Pmwset in steady state. That is the meaning of secondary control.