Transmission lines have different ratings for different ambient temperatures. Also different rating for normal operation and short time overload operation after contingencies. There are equipments in the breaker bay with different current rating, e.g. breaker, current transformer, switches.
From rev 34 there are twelve ratings, which is enough for the need of most users. You just use the number of ratings that are necessary for you needs.