Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

Take a look at the LDSHBL model in the MODELS.pdf documentation. For your example, you can add something similar to the following to your .dyr: 3, 'LDSHBL', '1', 49.5, 0.2, 0.5, 0, 0, 0, 0, 0, 0, 0.05 /