Unbalanced fault in PSSE requires sequence data to be loaded. If Balanced or Unbalanced I would recommend ASCC. You can change the output settings in Misc>OPTN>Short Circuit. You can set Physical, PerUnit, Rectangular, Polar there.
Thanks to 3phaseee.com for help on this one.