answered Jun 7 '17

perolofl gravatar image

Short answer: Converting the machines shall not change the bus voltages! INITIALIZED OUT OF LIMITS means that dynamic limits in the model do no match the load flow situation for the generator.

Exciter problems are often caused by overloaded generators (Pgen or Qgen) in loadflow or wrong dynamic data.

Governor problems are caused by overloaded Pgen in loadflow or wrong dynamic data.