Running a short circuit analysis and getting the results back can be difficult with the PSSE API. The documentation doesn't have any examples, and the API is a bit confusing. Here is how to do it:
ASCC_CURRENTS
ascc_currents in the pssarrays module will run the short circuit analysis and return the results in a custom made Python type that PSSE refers to as rlst.
# this script assumes you have already initalised PSSE and loaded a saved case.
import pssarrays
# create a subsystem of buses you will apply the fault to.
DOWNTOWN_SID = 1
psspy.bsys(sid=DOWNTOWN_SID, numbus=2, buses=[2001, 2002])
results = pssarrays.ascc_currents(sid=DOWNTOWN_SID,
all=0,
fltlg=1, # report on line to ground faults.
flat=0) # use prefault voltage from working case
This code will run a line to ground fault on two buses 2001 and 2002 and store the result in the scfilename file. We don't use flat start conditions, so the pre-fault voltage is the same as the one in the solved case.
Lets unpack the results variable to see what is inside:
# get the phase A current for this line to ground fault
phase_a = [i.ia for i in results.fltlg]
# and match the phase currents up against the faulted buses
fault_currents = zip(results.fltbus, phase_a)
print fault_currents
That final print statement should show something like this:
[(2001, (30.4 + 12.j) ),
(2002, (30.1 + 11j) ]
And now to answer your question
You asked about how to find the _maximum_. There are a number of things that contribute to a maximum fault level:- Prefault voltage (higher voltages have higher fault currents)
- All generation connected (each generator contributes to fault current)
- Buses at terminal stations are tied (will increase the fault current if the fault is downstream of the bus tie)
There are a few other things to watch for that will increase your fault currents unrealistically. If you model your SVC units as a synchronous condensor (like we do) then you need to replace it with an equivalent capacitor bank. SVC units behave like a capacitor during short circuits, not like a spinning machine.
Warning
I don't have a copy of PSSE here with me (and I wont for a few months). You should check that the code to get `phase_a` works. Let me know if it doesn't so I can update the answer with working code!Running a short circuit analysis and getting the results back can be is difficult with the PSSE API. The documentation doesn't have any examples, and the API It is a bit confusing. one of the most difficult things to do. Here is how to do it:
ASCC_CURRENTS
ascc_currents in the pssarrays module will run the short circuit analysis and return the results in a custom made Python type that PSSE refers to as rlst.
import pssarrays
# this script assumescreate a subsystem of buses you have already initalised PSSE and loaded a savedwill apply the fault case.
import pssarrays
# create a subsystem of buses you will apply the fault to.
DOWNTOWN_SID = 1
psspy.bsys(sid=DOWNTOWN_SID, numbus=2, buses=[=[2001, 2002])])
results = pssarrays.ascc_currents(sid=DOWNTOWN_SID,
all=0,
fltlg=1, # report on line to ground faults.
flat=0) # use prefault voltage from working case
This code will run a line to ground fault on two buses 2001 and 2002 and store the result in the scfilename file. We don't use flat start conditions, so the pre-fault voltage is the same as the one in the solved case.
Lets unpack the results variable to see what is inside:
# get the phase A current for this line to ground fault
phase_a = [i.ia for i in results.fltlg]
# and match the phase currents up against the faulted buses
fault_currents = zip(results.fltbus, phase_a)
print fault_currents
That final print statement should show something like this:
[(2001, (30.4 + 12.j) ),
(2002, (30.1 + 11j) ]
And now to answer your question
You asked about how to find the _maximum_. There are a number of things that contribute to a maximum fault level:- Prefault voltage (higher voltages have higher fault currents)
- All generation connected (each generator contributes to fault current)
- Buses at terminal stations are tied (will increase the fault current if the fault is downstream of the bus tie)
There are a few other things to watch for that will increase your fault currents unrealistically. If you model your SVC units as a synchronous condensor (like we do) then you need to replace it with an equivalent capacitor bank. SVC units behave like a capacitor during short circuits, not like a spinning machine.
Warning
I don't have a copy of PSSE here with me (and I wont for a few months). You should check that the code to get `phase_a` works. Let me know if it doesn't so I can update the answer with working code!Running a short circuit analysis is difficult with the PSSE API. It is one of the most difficult things to do. Here is how to do it:
ASCC_CURRENTS
ascc_currents in the pssarrays module will
- Use the
ascc_2API to
.sc) file
rlst..sc file with the pssarrays.ascc_currents
ASCC_2
import pssarrays
# create a subsystem of buses you will apply the fault to.
DOWNTOWN_SID = 1
scfilename = "kolkata-fault.sc"
psspy.bsys(sid=DOWNTOWN_SID, numbus=2, buses=[=[2001, 2002])
results = pssarrays])
ierr = psspy.ascc_currentsascc_2(sid=DOWNTOWN_SID,
all=0,
fltlg # only process buses inside DOWNTOWN_SID
status1=1, # report onsingle line to ground faultsfault.
flat=0scfile=scfilename) # use prefault voltage from working case
This code will run a line to ground fault on two buses 2001 and 2002 and store the result in the scfilename file. We don't use flat start conditions, so the pre-fault voltage is the same as the one in the solved case.
Lets unpack the ASCC_CURRENTS
ascc_currents in the pssarrays module will return the short circuit results variable to see what is inside:as Python data that we can use.
# get the phase A current for this line to ground fault
phase_a = [i.ia for i in results.fltlg]
# and match the phase currents up against the faulted buses
fault_currents = zip(results.fltbus, phase_a)
print fault_currentsimport pssarrays
results = pssarrays.ascc_currents(sid=DOWNTOWN_SID,
That final print statement should show something like this:
[(2001, (30.4 + 12.j) ),
(2002, (30.1 + 11j) ]
And now to answer your question
You asked about how to find the _maximum_. There are a number of things that contribute to a maximum fault level:- Prefault voltage (higher voltages have higher fault currents)
- All generation connected (each generator contributes to fault current)
- Buses at terminal stations are tied (will increase the fault current if the fault is downstream of the bus tie)
There are a few other things to watch for that will increase your fault currents unrealistically. If you model your SVC units as a synchronous condensor (like we do) then you need to replace it with an equivalent capacitor bank. SVC units behave like a capacitor during short circuits, not like a spinning machine.