  1. One of the infinite buses should be swing bus and the others should be type 2 with large reactive capacity, i.e. not hitting a reactive limit.
  2. You can select any scheduled voltage, not necessarily 1 pu.
  3. Correct
  4. Correct
  5. Correct

If you want the bus to be infinite in dynamics choose a high Mbase and low Xsource for the generator.