- One of the infinite buses should be swing bus and the others should be type 2 with large reactive capacity, i.e. not hitting a reactive limit.
- You can select any scheduled voltage, not necessarily 1 pu.
- Correct
- Correct
- Correct
If you want the bus to be infinite in dynamics choose a high Mbase and low Xsource for the generator.