You can use the short-circuit data retrieval APIs after SCMU. image description image description

You can use the short-circuit data retrieval APIs after SCMU. image description image descriptionSCMU.

    scinit()
    Use this API to initialize the short-circuit data retrieval APIs. It must be called when PSS(R)E is at the power flow activity level and must follow each execution of activity SCMU. Can be followed by SCBUS2, SCBRN2, SC3WND and SCMAC2 calls. SCDONE must be called after executing these and before any other calls or PSS(R)E activities can be executed.

    Python syntax:

    ierr = scinit()

    where:


    Integer IERR      Is the error code (output):
    IERR = 0 No error.
    IERR = 1 Sequence data not in case.
    IERR = 2 Unable to access SCMU results; one of the following occurred:
    *  No SCMU results file is open.
    *  SCMU results are not compatible with the working case.
    *  Error reading the SCMU results file.

You can use the short-circuit data retrieval APIs after SCMU.

 scinit()
 Use this API to initialize the short-circuit data retrieval APIs. It must be called when PSS(R)E is at the power flow activity level and must follow each execution of activity SCMU. Can be followed by SCBUS2, SCBRN2, SC3WND and SCMAC2 calls. SCDONE must be called after executing these and before any other calls or PSS(R)E activities can be executed.

    Python syntax:

    ierr = scinit()

    where:
     Integer IERR      Is the error code (output):
    IERR = 0 No error.
    IERR = 1 Sequence data not in case.
    IERR = 2 Unable to access SCMU results; one of the following occurred:
    *  No SCMU results file is open.
    *  SCMU results are not compatible with the working case.
    *  Error reading the SCMU results file.

scbus2(ibus=None, string=None)
Returns complex bus voltages and currents following activity SCMU.

    Python syntax:

    ierr, cmpval = scbus2(ibus, string)

    where:
    Integer IBUS      Bus number (input).
    Character STRING     String indicating the quantity desired (input):
    'VPOS'   Positive sequence voltage.
    'VNEG'   Negative sequence voltage.
    'VZERO'  Zero sequence voltage.
    'VA'  A-phase voltage.
    'VB'  B-phase voltage.
    'VC'  C-phase voltage.
    'SHUNTP' Positive sequence shunt current.
    'SHUNTN' Negative sequence shunt current.
    'SHUNTZ' Zero sequence shunt current.
    'SHUNTA' A-phase shunt current.
    'SHUNTB' B-phase shunt current.
    'SHUNTC' C-phase shunt current.
    'FAULTP' Positive sequence fault current.
    'FAULTN' Negative sequence fault current.
    'FAULTZ' Zero sequence fault current.
    'FAULTA' A-phase fault current.
    'FAULTB' B-phase fault current.
    'FAULTC' C-phase fault current.
    Real P      Real component of the complex value indicated by STRING (output).
    Real Q      Reactive component of the complex value indicated by STRING (output).
    Complex CMPVAL    Complex value indicated by STRING (output).
    Integer IERR      Is the error code (output):
    IERR = 0 No error; 'P,Q' or 'CMPVAL' returned.
    IERR = 1 'SCINIT' not successfully called; 'P,Q' or 'CMPVAL' unchanged.
    IERR = 2 Bus not found; 'P,Q' or 'CMPVAL' unchanged.
    IERR = 3 Bad value of 'STRING'; 'P,Q' or 'CMPVAL' unchanged.
    IERR = 4 Bus disconnected; 'P,Q' or 'CMPVAL' of (0.,0.) returned.
    IERR = 5 Bus not faulted; 'P,Q' or 'CMPVAL' of (0.,0.) returned.