Do the following:

  1. Split the load bus and move the load to be tripped to the new bus (LBUS). Change the bus code to 2.
  2. Add a dummy generator at the load bus with Mbase=0.01, Qmax = Qmin = 0.
  3. Add dynamic model GENCLS to the dummy generator with H=0.001.
  4. Add dynamic model FRQDCAT with ICON(M)=LBUS, ICON(M+1)=LBUS and ICON(M+2)=generator id.

The load is now connected to a fictitious generator bus and model FRQDCAT can be used to trip the bus at overfrequency.