| 1 | initial version |
When using PLBVFU1, intention is to apply the required playback at the POC. Use an infinite generator with a very low impedance SCR(9999) branch to play the same voltage and frequency at the POC. Also the Playback generator is a voltage source behind an impedance. To get the same voltage at the terminal make your infinite machine MVA higher or reduce machine impedance (specifically X).