First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
1 | initial version |
Hi, Stokes CB. When I need to do this kind of event, I add a Plant Controller, for example, PLNTBU1 model. This model controls the operation mode, of a wind farm, a PV plant, or convencional plant with some generators. In the case of WF or PV, this model represent the power plant controller. With this model you will be able to make a V or Q step. First of all you have to define the kind of control your wind turbine will do, for example, V, P, Q control. Then, you can start a simulation, and then make a change at the corresponding VAR, to change, in your case, the reference of Q, Qref. That will introduce a step in Q, which is your goal.