Unbalanced faults can be simulated if sequence data (zero and negative sequence) are present in the saved case.

  • Initialise simulation

  • Run to time t1

  • Apply unbalanced bus fault and select "Line-to-ground" fault

  • Run to time t2

  • Clear fault

  • Apply unbalanced bus fault and select "Line-to-line or
    Line-to-line-to-ground" fault

  • Clear fault

  • Run to t4