Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

Dynamic setups are always unique. Some comments:

- Make sure that the steady state case converges and there is no limit violation on dynamic devices (gens) 
- The "Initial Condition Suspect" table shows model IEEET1 being reported but its dyr data is not posted in the section above.
- Q1: To tune the IEEET1 exciter, check if changing the value of a gain parameter(s) like k2 would resolve the problem.  See model block diagram in manual "Models".
- Q2: Use the plant controller (walk before run principle)
- Q3: The original run of SMIB_BESS does not have an initial condition problem. Go to first comment.