Tap positions
When I change tap postion in stady state mode nothing happend. I add controlled bus number an put control mode 1- Voltage, but when I change tap position, voltage dont change.
Does anyone now why?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
When I change tap postion in stady state mode nothing happend. I add controlled bus number an put control mode 1- Voltage, but when I change tap position, voltage dont change.
Does anyone now why?
Asked: 2021-04-16 01:45:29 -0500
Seen: 482 times
Last updated: Apr 16 '21
Calculate the impedance from one bus to all others
Confusion around base kV and PU voltage
Power flow results of SMIB in PSS/E do not match the hand calculations
Relative Voltage Angle for Dynamics
How can you get the values of the sensitivity matrix?
How to simulate secondary frequency control in pss/e
What do you change? There is no parameter for ”tap position”.
To simulate a tap position change you would need to change the winding voltage for the transformer winding that has the tap.