Translate No load FAT data to SAT2T model in PSS\e

asked 2023-12-11 09:38:47 -0500

brock gravatar image

I have the factory test report that have the no load test with voltages applied from .8 pu to 1.1 pu voltage and the corresponding currents? How is that translated to the SAT2T model in PSS\e dynamics. I know the calc the flux linkage you must convert the voltage from rms by multiplying by the square root of two and I believe you will divide that value by 2pif but the formula on page 879 of the models documentation is confusing to calculate the values the model wants for the voltage access.

edit retag flag offensive close merge delete