Ask Your Question

Revision history [back]

click to hide/show revision 1
initial version

I haven't used this model but I believe you will get this message if PGEN<>0 in your saved case. The model is most probably not written to handle a situation with PGEN>0 without an error message.

Normally, PGEN should be set to zero in the load flow since a battery storage is (normally) not used at steady state operation. It should be activated during disturbances in the system, i.e. during the dynamic simulation but not before the start of the simulation. You can control the MW output of CBEST with VAR(L).

I think the model may work correctly, even with this warning at initialisation. Try to run a simulation and plot the results to see if the model behaviour is what you expect.