2020-10-09 07:23:14 -0500 commented answer Dynamic models of the generating units far away from the area of interest

Thank you very much sir!

2020-10-09 07:20:50 -0500 received badge  Famous Question (source)
2020-10-07 21:36:15 -0500 received badge  Notable Question (source)
2020-10-06 08:40:29 -0500 received badge  Popular Question (source)
2020-10-05 04:15:34 -0500 commented question Dynamic models of the generating units far away from the area of interest

Thank you very much! Helped a lot!

2020-10-04 13:02:46 -0500 asked a question Dynamic models of the generating units far away from the area of interest

Hi guys,

I have a raw file which contains over 20000 synchronous generating units and has over 100 000 buses. The raw file is like really really big (like half of USA or Europe).

I should run dynamic simulations (tripping lines & generating units as well as bus/line faults, thus analyzing the voltage and rotor angle stability as well as measuring like 15 critical clearing times) in an power system area which is only a small part of the wide-area system and contains approximately 100 gen. units for which I have a good data for a fine tuning of the GENROU/GENSAL, HYGOV/TGOV1/GAST, SEXS/SCRX models of generators, turbine governors and excitation systems, respectively. The dynamic simulations and the units of interest are only limited to the area I described above.

My questions are:

  1. What data in the dyr should I provide for the generators that are not a topic of interest and will not be analysed? (I don't even have enough data for them to be properly modelled) Maybe GENCLS with a classical H=3, D=0, or maybe, model them as infinity bus by setting H=0, D=0.

  2. Should I just leave such units without any dynamic models? Does that automatically mean that PSS-E will treat them as a negative load (of course represented by I-Y Norton equvivalent).

Thank you very much!

Kind regards,

Alex

2020-08-06 14:45:40 -0500 received badge  Taxonomist
2020-07-03 02:17:29 -0500 answered a question Generic model question

Jorge, even in the newest v35.1 there isn't the REPCMU1, even though it was mentioned to be released maybe an year or two ago.

2019-11-25 09:17:49 -0500 answered a question I need a PSSE Statcom (Facts) example

Hello,

I assume that you have to make some tests that include infinity bus (use GENCLS, H=0, D=0, Xsource=MBASE/ShortCircuitPower), then, a line, then, a STATCOM transformer, and then simply a STATCOM device (I recommend usage of FACTS device and not STATCOM as generator unit).

I don't know if the manuals in v34 have the same/similar numbering, but in v33.5 I would recommend you to:

-see 6.4.8 in PAGV1 and 5.2.1 & 6.3.16 in POM, regarding Load Flow analysis, and

-see 16.2 in Models and 24.8 in PAGV2, regarding dynamic behavior.

Kind regards!

2019-10-29 06:21:02 -0500 answered a question How to choose parameters of FACTS for reactive power compensation?

Hello,

See 6.4.8 in PAGV1 and 5.2.1 & 6.3.16 in POM regarding LF.

See 16.2 in Models and 24.8 in PAGV2 regarding dynamic behavior.

Kind regards!

2019-10-20 20:09:57 -0500 received badge  Famous Question (source)
2019-09-11 01:17:53 -0500 received badge  Famous Question (source)
2019-08-28 16:31:58 -0500 received badge  Famous Question (source)
2019-08-27 02:38:20 -0500 received badge  Famous Question (source)
2019-08-16 04:06:12 -0500 received badge  Notable Question (source)
2019-08-13 07:20:45 -0500 received badge  Notable Question (source)
2019-08-12 20:11:21 -0500 received badge  Popular Question (source)
2019-08-09 08:06:50 -0500 asked a question Models library (pdf) & PAGV2 (pdf) (newest version)

Hi!

Where can I find the newest version of the Models library and the Program Application Guide Volume 2 (for the newest version of PSS)? Can someone send me any link or pdf? I just want to compare them with an older version of PSS (v33).

Thank you!

Kind regards

2019-08-08 21:52:50 -0500 received badge  Popular Question (source)
2019-08-08 21:52:50 -0500 received badge  Notable Question (source)
2019-08-08 02:33:19 -0500 received badge  Popular Question (source)
2019-08-05 02:19:14 -0500 received badge  Famous Question (source)
2019-07-29 15:31:10 -0500 received badge  Notable Question (source)
2019-07-29 11:09:12 -0500 asked a question How to make a ramp function during the dynamic simulation for Paux in the CBEST

Guys, Is it possible to model a ramp function (or any other function) for the Paux in the CBEST model (or any auxiliary signal) during a dynamic simulation? For example I want Paux to be Paux(t)=4MW - (1 MW/60s )* t, for 0<= t < 480 s = 8 min - automated linear decrease of the Paux from 4 MW to -4 MW in a time interval of 8 min. Is it possible?

I already did the simulation by changing the Paux with a (1/60) MW decreament every second (the plot is step-wise), but there is soo much clicking... I want to automate the process, if possible.

Thank you very much!

Kind regards,

Alexander

2019-07-29 10:52:18 -0500 asked a question REPCAU1 + REECAU1

Hi guys!

I've been trying to make a BESS dynamic model which I'm going to use for a primary frequency regulation. By using PSS-E v33.4, I have combined the next three models: REGCAU1, REPCAU1 and REECAU1 (instead of REECCU1, since I don't have that model in my version of PSS) I've got two questions:

  1. Is there any chance that I could eliminate the hard coded restriction Ipmin=0 (just before Ipcmd in the block scheme) within the REECAU1 model? In the model REECCU1 there is no such restriction since that model is genuinely made for a 4 quadrant BESS P/Q control. Any suggestions, please?

  2. Within the REPCAU1 model, after I had started the dynamic simulation and the initial conditions had been ok, I've tried to make a step change on active power by changing the Plantref - the active power reference, but I am not sure if I can use that as some kind of an auxiliary signal Paux. For example, in the LF, I have Mbase = 4 MW and Pgen=4 MW. Ddn and Dup are 0, Kp=1 and Kpi=0.0001. During the initialization, the Plantref is set to 1 (P=4 MW on Mbase = 4 MW). But, where is the problem/misunderstanding: At the time t = 1 s, I change Plant_ref to 0 and expect to get P=0, but instead of it, I get P=0.5 pu (on Mbase) = 0.02 (od SBASE = 100 MVA). I cannot see what is the problem... It is like, for every wanted active power change, I get half of it. Any suggestions, please? Some .pdf guide is welcome (except the MODELS and PAGV2 PSS help...)

The parameters are:

4,'USRMDL',1,'REGCAU1',101,1,1,14,3,4,1, 0.02,10.0,0.9,0.5,1.22, 1.2,0.8,0.4,-1.3,0.02,0.7,9999.0,-9999.0,1.0 /

4,'USRMDL',1,'REECAU1',102,0,6,45,6,9, 0,0,1,1,0,1, -99.0,99.0,0.0,-0.05,0.05,0.0,1.05,-1.05,0.0, 0.0, 0.0, 0.0, 0.05, 0.436,-0.436,1.1,0.9,0.0,0.1,0.0,40.0, 0.0, 0.02,99.0,-99.0,1.0,-1.0,1.3, 0.02,0.0,0.0,0.0,0.0,0.0, 0.0,0.0,0.0,0.0,0.0,0.0,0.0,0.0,0.0,0.0,0.0 /

4,'USRMDL', 1, 'REPCAU1',107, 0, 7, 27, 7, 9, 0, 0, 0, 0, 1, 0, 1, 0.02, 0.0, 0.0001, 0, 0.05, 0, 0, 0, 0, 0.1, -0.1, 0, 0, 0.75, -0.75, 1, 0.0001, 0.02, -0.0006, 0.0006, 99, -99, 1, -1, 0.1, 0, 0 //

Thank you very much!

Kind regards,

Alexander

2019-07-23 01:52:59 -0500 received badge  Popular Question (source)
2019-07-23 01:52:13 -0500 received badge  Enthusiast
2019-07-19 08:38:46 -0500 asked a question Axis transform (e.g. f[pu] ->f[Hz] or P[pu] -> P[MW]) via PlotPackage and not by PSSPLT

Guys, is it possible to rescale and consequently change the units of an axis within the PlotPackage (by simply using Editing window)?

For example, I wanna change the f(t) [pu] -> f(t) [Hz) and P [pu] -> P[MW].

Thank you!

2019-06-19 07:29:03 -0500 received badge  Notable Question (source)
2019-06-19 02:13:34 -0500 answered a question How to control Paux within CBEST via PAUX1T (PSS-E v33.5)

Thank you perolofl!

Is there any chance that I could add the CBEST model into the list of FACTS devices? Or, maybe write a CONEC? How would that CONEC look?

Thank you in advance!

2019-06-19 02:10:41 -0500 received badge  Scholar (source)
2019-06-19 02:09:58 -0500 received badge  Popular Question (source)
2019-06-13 05:44:23 -0500 received badge  Editor (source)
2019-06-13 05:43:42 -0500 asked a question How to control Paux within CBEST via PAUX1T (PSS-E v33.5)

Dear experts, I am trying to link the auxiliary signal model PAUX1T with the CBEST model in order to create a simple frequency primary regulator. In the .dyr file I have:

4, 'CBEST', 1, 4.0000, 1.1000, 0.90000, 1.0000, 1.0000, 0.0000, 0.0000, 0.50000E-01, 0.0000, 10.000, -10.000, 0.50000E-02/

4, 'PAUX1T', 4, 1, 7, 0.01, 0.005, -20, 4, -4 /

(I am whatching the frequency of the 7th bus)

But still, when I activate the dyr file in PSS-E, I cannot see the PAUX1T anywhere. I've been reading that many have been using such combination of models, but I don't know how is that possible, since CBEST is a generator model and not a FACTS device (or two-terminal dc line, or multi-terminal dc line, or VSC dc line).

I am looking forward for your help!

Thank you in advance!