Results of optimal power flow

Can someone help me understand the results of the optimal power flow, specifically the Summary Table for the Tap Changing Transformers?

The tap changing transformers are held at fixed position in the OPF settings but I'm not sure why the voltage at each bus changes

Summary Table for Tap Changing Transformers:

From Bus kV Area Zone Voltage Ratio Minimum MW Flow Sensitivity To Bus kV Area Zone Voltage Change Maximum MV Flow Tap Volt


652 BUS 652 1602 1.02675 1.02500 F 0.90000 -3.910 1.00817 659 BUS 659 699 0.99487 1.10000 0.724

655 BUS 652 1678 1.04511 1.00000 F 0.90000 1.870 -79.80223 700 BUS 652 1678 1.04999u 1.10000 -0.964 -76.70278

655 BUS 652 1678 1.01109 1.00000 F 0.90000 3.834 1.04798 700 BUS 652 1678 1.02065 1.10000 -1.905

655 BUS 652 1678 0.97999 1.00000 F 0.90000 10.283 1.67920 700 BUS 652 1678 0.97459 1.10000 0.760

655 BUS 652 1678 0.98211 1.00000 F 0.90000 8.775 1.89995 700 BUS 652 1678 0.98177 1.10000 -0.071

655 BUS 652 1678 1.02741 1.00000 F 0.90000 8.472 -331.11280 700 BUS 652 1678 1.05000u 1.10000 -7.958 -313.73414

655 BUS 652 1678 0.95000L 1.00000 F 0.90000 25.618 27.02947 266.19141 700 BUS 652 1678 0.95007L 1.10000 0.854 6.42012

655 BUS 652 1678 0.95000L 1.00000 F 0.90000 21.299 21.03029 266.19141 700 BUS 652 1678 0.95720 1.10000 0.035

655 BUS 652 1678 0.95831 1.00000 F 0.90000 6.423 3.28565 700 BUS 652 1678 0.96161 1.10000 -0.347

655 BUS 652 1678 0.95819 1.00000 F 0.90000 9.726 57.39743 700 BUS 652 1678 0.95000L 1.10000 1.300 56.81060

Results of optimal power flow

Can someone help me understand the results of the optimal power flow, specifically the Summary Table for the Tap Changing Transformers?

The tap changing transformers are held at fixed position in the OPF settings but I'm not sure why the voltage at each bus changes

Summary Table for Tap Changing Transformers:

From Bus kV Area Zone Voltage Ratio Minimum MW Flow Sensitivity To Bus kV Area Zone Voltage Change Maximum MV Flow Tap Volt


652 BUS 652 1602 1.02675 1.02500 F 0.90000 -3.910 1.00817 659 BUS 659 699 0.99487 1.10000 0.724

655 BUS 652 1678 1.04511 1.00000 F 0.90000 1.870 -79.80223 700 BUS 652 1678 1.04999u 1.10000 -0.964 -76.70278

655 BUS 652 1678 1.01109 1.00000 F 0.90000 3.834 1.04798 700 BUS 652 1678 1.02065 1.10000 -1.905

655 BUS 652 1678 0.97999 1.00000 F 0.90000 10.283 1.67920 700 BUS 652 1678 0.97459 1.10000 0.760

655 BUS 652 1678 0.98211 1.00000 F 0.90000 8.775 1.89995 700 BUS 652 1678 0.98177 1.10000 -0.071

655 BUS 652 1678 1.02741 1.00000 F 0.90000 8.472 -331.11280 700 BUS 652 1678 1.05000u 1.10000 -7.958 -313.73414

655 BUS 652 1678 0.95000L 1.00000 F 0.90000 25.618 27.02947 266.19141 700 BUS 652 1678 0.95007L 1.10000 0.854 6.42012

655 BUS 652 1678 0.95000L 1.00000 F 0.90000 21.299 21.03029 266.19141 700 BUS 652 1678 0.95720 1.10000 0.035

655 BUS 652 1678 0.95831 1.00000 F 0.90000 6.423 3.28565 700 BUS 652 1678 0.96161 1.10000 -0.347

655 BUS 652 1678 0.95819 1.00000 F 0.90000 9.726 57.39743 700 BUS 652 1678 0.95000L 1.10000 1.300 56.81060