1 | initial version |
If between POI (bus 1000) where you are regulating and measurement point (bus 5), there is a interconnection line, should REPCA model filled as follow? 5 Remote bus number or 0 for local voltage control 5 Monitored branch FROM bus 1000 Monitored branch TO bus '1' Monitored branch ID (enter within single quotes) 0 VCFlag, droop flag (0: with droop,1: line drop compensation) 1 RefFlag, flag for V or Q control(0: Q control, 1: V control) 1 Fflag, 0: disable frequency control, 1: enable
Altough your regulating point is 1000, you only have measurement feedback from 5.
Is Rc, Xc and Kc used to compensate the differenve between points? I see it exist for V but not for Q control. Maybe I understand wrongly for what Rc, Xc and Kc are implemented.
Should these values modified from thegiven by the manufacturer based on plant characteristics?