I modeled a single machine infinite bus (SMIB) network with the following data:
Sb = 100 MVA f = 60 Hz P = 1 pu Pf = 0.95 Xl1 = j0.2 pu (transmission line 1 reactance) Xl2 = jo.3 pu (transmission line 2 reactance) Generator X'd = 0.3 pu
I added two buses, two lines and two generators. Bus 1 consisted of generator whose Pgen was set to 1 MW, Qmax=Qmin was set to 0.328 Mvar based on pf=0.95, and X Source set to 0.3. To model an infinite bus, I set the type code of bus 2 to 3 (swing) with generator X Source (pu) set to 99999. For transmission lines, pu reactances were added as Line X (pu).
I was interested in the bus 1 Voltage (pu) and Angle (degree). The results I got in PSS/E were: Voltage (pu) = 1.0004 Angle (degree) = 0.07
However, the results I got by hand calculations were different: Voltage (pu) = 1.213 Angle (degree) = 20.25
Where did I make the mistake? 1. Did I model the infinite bus incorrectly? 2. Did I add transient reactance X'd incorrectly? 3. Or any other mistake?
Any help will be highly appreciated. Thanks.
2 | No.2 Revision |
I modeled a single machine infinite bus (SMIB) network with the following data:
Sb = 100 MVA f = 60 Hz P = 1 pu Pf = 0.95 Xl1 = j0.2 pu (transmission line 1 reactance) Xl2 = jo.3 pu (transmission line 2 reactance) Generator X'd = 0.3 pu
I added two buses, two lines and two generators. Bus 1 consisted of generator whose Pgen was set to 1 MW, Qmax=Qmin was set to 0.328 Mvar based on pf=0.95, and X Source set to 0.3. To model an infinite bus, I set the type code of bus 2 to 3 (swing) with generator X Source (pu) set to 99999. For transmission lines, pu reactances were added as Line X (pu).
I was interested in the bus 1 Voltage (pu) and Angle (degree). The results I got in PSS/E were: Voltage (pu) = 1.0004 Angle (degree) = 0.07
However, the results I got by hand calculations were different: Voltage (pu) = 1.213 Angle (degree) = 20.25
Where did I make the mistake?
1.
Any help will be highly appreciated. Thanks.
3 | No.3 Revision |
I modeled a single machine infinite bus (SMIB) network with the following data:
Sb = 100 MVA
MVA;
f = 60 Hz
Hz;
P = 1 pu
pu;
Pf = 0.95
0.95;
Xl1 = j0.2 pu (transmission line 1 reactance)
reactance);
Xl2 = jo.3 pu (transmission line 2 reactance)
reactance);
Generator X'd = 0.3 pupu;
I added two buses, two lines and two generators. Bus 1 consisted of generator whose Pgen was set to 1 MW, Qmax=Qmin was set to 0.328 Mvar based on pf=0.95, and X Source set to 0.3. To model an infinite bus, I set the type code of bus 2 to 3 (swing) with generator X Source (pu) set to 99999. For transmission lines, pu reactances were added as Line X (pu).
I was interested in the bus 1 Voltage (pu) and Angle (degree). The results I got in PSS/E were: Voltage (pu) = 1.0004 Angle (degree) = 0.07
However, the results I got by hand calculations were different: Voltage (pu) = 1.213 Angle (degree) = 20.25
Where did I make the mistake?
Any help will be highly appreciated. Thanks.