Hi All,
Thanks for reading the question.
I am testing the composite model in IEEE 9 bus system, while the CLODxx model is not converged in my case. I don't know what is wrong with my operation, I really appreciate if you give me some suggestions. My raw file and dyr files are pasted below, you are welcome to try.
raw file:
0, 100.00, 32, 0, 1, 60.00 / PSS(R)E-32.2 MON, DEC 08 2014 17:27
IEEE 9 BUS CASE - 3G - 3L
1,'BUS1 ', 16.5000,3, 1, 1, 1,1.04000, 0.0000
2,'BUS2 ', 18.0000,2, 2, 2, 1,1.02500, 9.2800
3,'BUS3 ', 13.8000,2, 2, 3, 1,1.02500, 4.6648
4,'BUS4 ', 230.0000,1, 1, 1, 1,1.02579, -2.2168
5,'BUS5 ', 230.0000,1, 1, 4, 2,0.99563, -3.9888
6,'BUS6 ', 230.0000,1, 1, 5, 2,1.01265, -3.6874
7,'BUS7 ', 230.0000,1, 2, 2, 1,1.02577, 3.7197
8,'BUS8 ', 230.0000,1, 2, 6, 2,1.01588, 0.7275
9,'BUS9 ', 230.0000,1, 2, 3, 1,1.03235, 1.9667
0 / END OF BUS DATA, BEGIN LOAD DATA
5,'1 ',1, 1, 1, 125.000, 50.000, 0.000, 0.000, 0.000, 0.000, 1,1
6,'1 ',1, 1, 1, 90.000, 30.000, 0.000, 0.000, 0.000, 0.000, 1,1
8,'1 ',1, 1, 1, 100.000, 35.000, 0.000, 0.000, 0.000, 0.000, 1,1
0 / END OF LOAD DATA, BEGIN FIXED SHUNT DATA
0 / END OF FIXED SHUNT DATA, BEGIN GENERATOR DATA
1,'1 ', 71.641, 27.046, 300.000, -300.000,1.04000, 0, 260.000, 1.00000E-4, 1.00000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 250.000, 10.000, 1,1.0000
2,'1 ', 163.000, 6.654, 300.000, -300.000,1.02500, 0, 310.000, 1.00000E-4, 2.10000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 300.000, 10.000, 1,1.0000
3,'1 ', 85.000, -10.860, 300.000, -300.000,1.02500, 0, 280.000, 1.00000E-4, 2.10000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 270.000, 10.000, 1,1.0000
0 / END OF GENERATOR DATA, BEGIN BRANCH DATA
4, 5,'1 ', 1.00000E-2, 8.50000E-2, 0.17600, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
4, 6,'1 ', 1.70000E-2, 9.20000E-2, 0.15800, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
5, 7,'1 ', 3.20000E-2, 1.61000E-1, 0.30600, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
6, 9,'1 ', 3.90000E-2, 1.70000E-1, 0.35800, 150.00, 150.00, 150.00, 0.00000, 0.00000, 0.00000, 0.00000,1,2, 0.00, 1,1.0000
7, 8,'1 ', 8.50000E-3, 7.20000E-2, 0.14900, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
8, 9,'1 ', 1.19000E-2, 1.00800E-1, 0.20900, 150.00, 150.00, 150.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
0 / END OF BRANCH DATA, BEGIN TRANSFORMER DATA
1, 4, 0,'T1',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 5.76000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
2, 7, 0,'T2',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 6.25000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
9, 3, 0,'T3',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 5.86000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
0 / END OF TRANSFORMER DATA, BEGIN AREA DATA
1, 1, 50.000, 10.000,'AREA1 '
2, 2, 50.000, 10.000,'AREA2 '
0 / END OF AREA DATA, BEGIN TWO-TERMINAL DC DATA
0 / END OF TWO-TERMINAL DC DATA, BEGIN VSC DC LINE DATA
0 / END OF VSC DC LINE DATA, BEGIN IMPEDANCE CORRECTION DATA
0 / END OF IMPEDANCE CORRECTION DATA, BEGIN MULTI-TERMINAL DC DATA
0 / END OF MULTI-TERMINAL DC DATA, BEGIN MULTI-SECTION LINE DATA
0 / END OF MULTI-SECTION LINE DATA, BEGIN ZONE DATA
1,'ZONE1 '
2,'ZONE2 '
3,'ZONE3 '
4,'ZONE4 '
5,'ZONE5 '
6,'ZONE6 '
0 / END OF ZONE DATA, BEGIN INTER-AREA TRANSFER DATA
0 / END OF INTER-AREA TRANSFER DATA, BEGIN OWNER DATA
1,'OWNER1 '
2,'OWNER2 '
0 / END OF OWNER DATA, BEGIN FACTS DEVICE DATA
0 / END OF FACTS DEVICE DATA, BEGIN SWITCHED SHUNT DATA
0 / END OF SWITCHED SHUNT DATA, BEGIN GNE DATA
0 / END OF GNE DATA
Q
dyr file:
// IEEE_9bus.dyr
1 'GENSAL' 1 8.96 0.05 0.05 9.55 1.60 0.3615 0.24 0.1508 0.10 0.06 1.01 1.02 /
2 'GENROU' 1 6.00 0.05 0.535 0.05 3.33 0.67 1.72 1.66 0.23 0.37 0.21 0.10 1.01 1.02 /
3 'GENROU' 1 5.89 0.05 0.60 0.05 2.35 0.47 1.68 1.61 0.23206 0.32 0.21 0.1536 1.01 1.02 /
// exciter
1 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
2 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
3 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
// governor
1, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
2, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
3, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
// stabilizer
1,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
2,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
3,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
// complex load model 1 large motor 2small motor 3transformer exciting current
// 4 discharge lighting 5constant power 6 KP of remaining 7 Branch R 8Branch X
0, 'CLODAL',1, 5,50,1,15,10,2,0.01,0.8,/
Thanks in advance!
Gary
| 2 | No.2 Revision |
Hi All,
Thanks for reading the question.
I am testing the composite model in IEEE 9 bus system, while the CLODxx model is not converged in my case. when I initialize it for transient simulation. The case works fine without the dynamic load model (i.e., just converter the load to ZIP before running the transient simulation). I don't know what is wrong with my operation, case.
I really appreciate if you give me some suggestions. My raw file and dyr files are pasted below, you are welcome to try.
raw file:
0, 100.00, 32, 0, 1, 60.00 / PSS(R)E-32.2 MON, DEC 08 2014 17:27
IEEE 9 BUS CASE - 3G - 3L
1,'BUS1 ', 16.5000,3, 1, 1, 1,1.04000, 0.0000
2,'BUS2 ', 18.0000,2, 2, 2, 1,1.02500, 9.2800
3,'BUS3 ', 13.8000,2, 2, 3, 1,1.02500, 4.6648
4,'BUS4 ', 230.0000,1, 1, 1, 1,1.02579, -2.2168
5,'BUS5 ', 230.0000,1, 1, 4, 2,0.99563, -3.9888
6,'BUS6 ', 230.0000,1, 1, 5, 2,1.01265, -3.6874
7,'BUS7 ', 230.0000,1, 2, 2, 1,1.02577, 3.7197
8,'BUS8 ', 230.0000,1, 2, 6, 2,1.01588, 0.7275
9,'BUS9 ', 230.0000,1, 2, 3, 1,1.03235, 1.9667
0 / END OF BUS DATA, BEGIN LOAD DATA
5,'1 ',1, 1, 1, 125.000, 50.000, 0.000, 0.000, 0.000, 0.000, 1,1
6,'1 ',1, 1, 1, 90.000, 30.000, 0.000, 0.000, 0.000, 0.000, 1,1
8,'1 ',1, 1, 1, 100.000, 35.000, 0.000, 0.000, 0.000, 0.000, 1,1
0 / END OF LOAD DATA, BEGIN FIXED SHUNT DATA
0 / END OF FIXED SHUNT DATA, BEGIN GENERATOR DATA
1,'1 ', 71.641, 27.046, 300.000, -300.000,1.04000, 0, 260.000, 1.00000E-4, 1.00000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 250.000, 10.000, 1,1.0000
2,'1 ', 163.000, 6.654, 300.000, -300.000,1.02500, 0, 310.000, 1.00000E-4, 2.10000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 300.000, 10.000, 1,1.0000
3,'1 ', 85.000, -10.860, 300.000, -300.000,1.02500, 0, 280.000, 1.00000E-4, 2.10000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 270.000, 10.000, 1,1.0000
0 / END OF GENERATOR DATA, BEGIN BRANCH DATA
4, 5,'1 ', 1.00000E-2, 8.50000E-2, 0.17600, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
4, 6,'1 ', 1.70000E-2, 9.20000E-2, 0.15800, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
5, 7,'1 ', 3.20000E-2, 1.61000E-1, 0.30600, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
6, 9,'1 ', 3.90000E-2, 1.70000E-1, 0.35800, 150.00, 150.00, 150.00, 0.00000, 0.00000, 0.00000, 0.00000,1,2, 0.00, 1,1.0000
7, 8,'1 ', 8.50000E-3, 7.20000E-2, 0.14900, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
8, 9,'1 ', 1.19000E-2, 1.00800E-1, 0.20900, 150.00, 150.00, 150.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
0 / END OF BRANCH DATA, BEGIN TRANSFORMER DATA
1, 4, 0,'T1',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 5.76000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
2, 7, 0,'T2',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 6.25000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
9, 3, 0,'T3',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 5.86000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
0 / END OF TRANSFORMER DATA, BEGIN AREA DATA
1, 1, 50.000, 10.000,'AREA1 '
2, 2, 50.000, 10.000,'AREA2 '
0 / END OF AREA DATA, BEGIN TWO-TERMINAL DC DATA
0 / END OF TWO-TERMINAL DC DATA, BEGIN VSC DC LINE DATA
0 / END OF VSC DC LINE DATA, BEGIN IMPEDANCE CORRECTION DATA
0 / END OF IMPEDANCE CORRECTION DATA, BEGIN MULTI-TERMINAL DC DATA
0 / END OF MULTI-TERMINAL DC DATA, BEGIN MULTI-SECTION LINE DATA
0 / END OF MULTI-SECTION LINE DATA, BEGIN ZONE DATA
1,'ZONE1 '
2,'ZONE2 '
3,'ZONE3 '
4,'ZONE4 '
5,'ZONE5 '
6,'ZONE6 '
0 / END OF ZONE DATA, BEGIN INTER-AREA TRANSFER DATA
0 / END OF INTER-AREA TRANSFER DATA, BEGIN OWNER DATA
1,'OWNER1 '
2,'OWNER2 '
0 / END OF OWNER DATA, BEGIN FACTS DEVICE DATA
0 / END OF FACTS DEVICE DATA, BEGIN SWITCHED SHUNT DATA
0 / END OF SWITCHED SHUNT DATA, BEGIN GNE DATA
0 / END OF GNE DATA
Q
dyr file:
// IEEE_9bus.dyr
1 'GENSAL' 1 8.96 0.05 0.05 9.55 1.60 0.3615 0.24 0.1508 0.10 0.06 1.01 1.02 /
2 'GENROU' 1 6.00 0.05 0.535 0.05 3.33 0.67 1.72 1.66 0.23 0.37 0.21 0.10 1.01 1.02 /
3 'GENROU' 1 5.89 0.05 0.60 0.05 2.35 0.47 1.68 1.61 0.23206 0.32 0.21 0.1536 1.01 1.02 /
// exciter
1 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
2 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
3 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
// governor
1, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
2, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
3, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
// stabilizer
1,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
2,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
3,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
// complex load model 1 large motor 2small motor 3transformer exciting current
// 4 discharge lighting 5constant power 6 KP of remaining 7 Branch R 8Branch X
0, 'CLODAL',1, 5,50,1,15,10,2,0.01,0.8,/
Thanks in advance!
Gary
| 3 | No.3 Revision |
Hi All,
Thanks for reading the question.
I am testing the composite model in IEEE 9 bus system, while the CLODxx model is not converged when I initialize it for transient simulation. The case works fine without the dynamic load model (i.e., just converter convert the load to ZIP before running the transient simulation). I don't know what is wrong with my case.
I really appreciate if you give me some suggestions. My raw file and dyr files are pasted below, you are welcome to try.
raw file:
0, 100.00, 32, 0, 1, 60.00 / PSS(R)E-32.2 MON, DEC 08 2014 17:27
IEEE 9 BUS CASE - 3G - 3L
1,'BUS1 ', 16.5000,3, 1, 1, 1,1.04000, 0.0000
2,'BUS2 ', 18.0000,2, 2, 2, 1,1.02500, 9.2800
3,'BUS3 ', 13.8000,2, 2, 3, 1,1.02500, 4.6648
4,'BUS4 ', 230.0000,1, 1, 1, 1,1.02579, -2.2168
5,'BUS5 ', 230.0000,1, 1, 4, 2,0.99563, -3.9888
6,'BUS6 ', 230.0000,1, 1, 5, 2,1.01265, -3.6874
7,'BUS7 ', 230.0000,1, 2, 2, 1,1.02577, 3.7197
8,'BUS8 ', 230.0000,1, 2, 6, 2,1.01588, 0.7275
9,'BUS9 ', 230.0000,1, 2, 3, 1,1.03235, 1.9667
0 / END OF BUS DATA, BEGIN LOAD DATA
5,'1 ',1, 1, 1, 125.000, 50.000, 0.000, 0.000, 0.000, 0.000, 1,1
6,'1 ',1, 1, 1, 90.000, 30.000, 0.000, 0.000, 0.000, 0.000, 1,1
8,'1 ',1, 1, 1, 100.000, 35.000, 0.000, 0.000, 0.000, 0.000, 1,1
0 / END OF LOAD DATA, BEGIN FIXED SHUNT DATA
0 / END OF FIXED SHUNT DATA, BEGIN GENERATOR DATA
1,'1 ', 71.641, 27.046, 300.000, -300.000,1.04000, 0, 260.000, 1.00000E-4, 1.00000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 250.000, 10.000, 1,1.0000
2,'1 ', 163.000, 6.654, 300.000, -300.000,1.02500, 0, 310.000, 1.00000E-4, 2.10000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 300.000, 10.000, 1,1.0000
3,'1 ', 85.000, -10.860, 300.000, -300.000,1.02500, 0, 280.000, 1.00000E-4, 2.10000E-1, 0.00000E+0, 0.00000E+0,1.00000,1, 100.0, 270.000, 10.000, 1,1.0000
0 / END OF GENERATOR DATA, BEGIN BRANCH DATA
4, 5,'1 ', 1.00000E-2, 8.50000E-2, 0.17600, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
4, 6,'1 ', 1.70000E-2, 9.20000E-2, 0.15800, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
5, 7,'1 ', 3.20000E-2, 1.61000E-1, 0.30600, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
6, 9,'1 ', 3.90000E-2, 1.70000E-1, 0.35800, 150.00, 150.00, 150.00, 0.00000, 0.00000, 0.00000, 0.00000,1,2, 0.00, 1,1.0000
7, 8,'1 ', 8.50000E-3, 7.20000E-2, 0.14900, 250.00, 250.00, 250.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
8, 9,'1 ', 1.19000E-2, 1.00800E-1, 0.20900, 150.00, 150.00, 150.00, 0.00000, 0.00000, 0.00000, 0.00000,1,1, 0.00, 1,1.0000
0 / END OF BRANCH DATA, BEGIN TRANSFORMER DATA
1, 4, 0,'T1',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 5.76000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
2, 7, 0,'T2',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 6.25000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
9, 3, 0,'T3',1,1,1, 0.00000E+0, 0.00000E+0,2,' ',1, 1,1.0000
0.00000E+0, 5.86000E-2, 100.00
1.00000, 0.000, 0.000, 0.00, 0.00, 0.00, 0, 0, 1.10000, 0.90000, 1.10000, 0.90000, 33, 0, 0.00000, 0.00000, 0.000
1.00000, 0.000
0 / END OF TRANSFORMER DATA, BEGIN AREA DATA
1, 1, 50.000, 10.000,'AREA1 '
2, 2, 50.000, 10.000,'AREA2 '
0 / END OF AREA DATA, BEGIN TWO-TERMINAL DC DATA
0 / END OF TWO-TERMINAL DC DATA, BEGIN VSC DC LINE DATA
0 / END OF VSC DC LINE DATA, BEGIN IMPEDANCE CORRECTION DATA
0 / END OF IMPEDANCE CORRECTION DATA, BEGIN MULTI-TERMINAL DC DATA
0 / END OF MULTI-TERMINAL DC DATA, BEGIN MULTI-SECTION LINE DATA
0 / END OF MULTI-SECTION LINE DATA, BEGIN ZONE DATA
1,'ZONE1 '
2,'ZONE2 '
3,'ZONE3 '
4,'ZONE4 '
5,'ZONE5 '
6,'ZONE6 '
0 / END OF ZONE DATA, BEGIN INTER-AREA TRANSFER DATA
0 / END OF INTER-AREA TRANSFER DATA, BEGIN OWNER DATA
1,'OWNER1 '
2,'OWNER2 '
0 / END OF OWNER DATA, BEGIN FACTS DEVICE DATA
0 / END OF FACTS DEVICE DATA, BEGIN SWITCHED SHUNT DATA
0 / END OF SWITCHED SHUNT DATA, BEGIN GNE DATA
0 / END OF GNE DATA
Q
dyr file:
// IEEE_9bus.dyr
1 'GENSAL' 1 8.96 0.05 0.05 9.55 1.60 0.3615 0.24 0.1508 0.10 0.06 1.01 1.02 /
2 'GENROU' 1 6.00 0.05 0.535 0.05 3.33 0.67 1.72 1.66 0.23 0.37 0.21 0.10 1.01 1.02 /
3 'GENROU' 1 5.89 0.05 0.60 0.05 2.35 0.47 1.68 1.61 0.23206 0.32 0.21 0.1536 1.01 1.02 /
// exciter
1 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
2 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
3 'IEEET1' 1 0.0 20.0 0.2 3.0 -3.0 1.0 0.314 0.063 0.35 0.0 2.8 0.3034 3.73 1.2884 /
// governor
1, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
2, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
3, 'IEESGO', 1, 25.0, 0,1.0,1.0,12.5, 0, 5.0,3.0,0.5, 1.0, 0,/
// stabilizer
1,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
2,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
3,'PSS2A',1,1,0,3,0,5,1,2,2,0,2,4,2,0.250,1,0.5,0.1,30,0.15,0.03,0.15,0.03,0.1,-0.1,/
// complex load model 1 large motor 2small motor 3transformer exciting current
// 4 discharge lighting 5constant power 6 KP of remaining 7 Branch R 8Branch X
0, 'CLODAL',1, 5,50,1,15,10,2,0.01,0.8,/
Thanks in advance!
Gary