1 | initial version |
what my operation process is:
1)open savnw.sav
2)click "Power Flow -> Solve", check in "Convert Generators" and "Convert/Reconstruct Loads"
3) click "Power Flow -> Covert Loads and Generator"
4)click "Power Flow -> Solution -> TYSL", check in "FACT"
5)open savnw.dyr
6)click "Dynamic -> Simulation -> Perform Simulation(STRT/RUN)"
7)create out file, click "Initiate", set 1s and run
8)Adding fault
When I add branch unbalance falut to other bus pair, it can be work;
but Bus-3001 to Bus3003, something wrong, the information in output bar like this:
Channel output file is "C:\Users\Yang\Documents\PTI\PSSE34\EXAMPLE\tt001.outx"
Using machine R and X' from fault analysis data
Diagonals = 23 Off-diagonals = 38 Maximum size = 58
Positive sequence network: Diagonals = 23 Off-diagonals = 38
Negative sequence network: Diagonals = 23 Off-diagonals = 38
Diagonals = 23 Off-diagonals = 32 Maximum size = 46
Bus 101 [NUC-A 21.600] is isolated in the zero sequence network
Bus 102 [NUC-B 21.600] is isolated in the zero sequence network
Bus 206 [URBGEN 18.000] is isolated in the zero sequence network
Bus 211 [HYDRO_G 20.000] is isolated in the zero sequence network
Bus 3011 [MINE_G 13.800] is isolated in the zero sequence network
Bus 3018 [CATDOG_G 13.800] is isolated in the zero sequence network
6 buses are isolated in the zero sequence network
Zero sequence network: Diagonals = 23 Off-diagonals = 32
Messages for api DIST_SPCB_FAULT_2
Terminated due to invalid fault specification or application: (003701)
Invalid branch circuit "1" from bus 3001 [MINE 230.00] to bus 3003 [S. MINE 230.00] (003702)
There is no path to ground at bus 3001 [MINE 230.00] (003713)
Output completed