I run a load flow for a case , it converges normally. When I try STRT and initializing the dynamic simulation , it does not converge as follows: '' NITIAL CONDITION LOAD FLOW USED 1 ITERATIONS
----------------------------- MACHINE INITIAL CONDITIONS ----------------------------- BUS#-SCT X-- NAME --X BASKV ID ETERM EFD POWER VARS P.F. ANGLE ID IQ 81201 C.T.M-G3 15.000 1 1.0195 2.3545 120.00 90.00 0.8000 38.31 0.7174 0.3229 81202 C.T.M-G4 15.000 1 1.0195 2.3545 120.00 90.00 0.8000 38.31 0.7174 0.3229 81212 JORF -G1 22.000 1 1.0825 2.6688 320.00 150.00 0.9055 57.59 0.7277 0.4224 81213 JORF -G2 22.000 1 1.0867 2.6748 320.00 149.51 0.9060 58.30 0.7224 0.4241 81214 JORF -G3 22.000 1 1.0825 2.5424 320.00 150.00 0.9055 57.54 0.7273 0.4230 81215 JORF -G4 22.000 1 1.0867 2.5484 320.00 149.51 0.9060 58.24 0.7220 0.4247 81250 PE OUALIDIA 33.000 1 1.1045 0.0000 32.00 2.71 0.9964 54.08 0.0687 0.8118 81266 PE TANGER 33.000 1 1.0500 0.0000 140.00 19.11 0.9908 5.62 0.1138 0.8333 81390 PV ZAGORA 60.000 1 1.0667 0.0000 27.00 -3.96 0.9894 19.60-0.0978 0.6661 81601 STEPIG1 13.800 1 1.0733 2.8671 160.00 80.00 0.8944 46.15 0.7240 0.4740 81602 STEPIG2 13.800 1 1.0717 2.8662 160.00 80.00 0.8944 45.98 0.7255 0.4740 81603 STEPIIG1 10.300 1 1.0657 2.1161 60.00 26.00 0.9175 37.98 0.4388 0.4289 81604 STEPIIG2 10.300 1 1.0659 2.1164 60.00 26.00 0.9175 38.00 0.4387 0.4288 81605 TAHADG1 21.000 1 1.0452 2.1825 380.00 38.31 0.9950 53.79 0.5719 0.4550 81720 C.T.SAFI G1 21.000 1 1.0588 2.1105 650.00 86.97 0.9912 85.26 0.6337 0.5039 81721 C.T.SAFI G2 21.000 1 1.0588 2.1105 650.00 86.97 0.9912 85.26 0.6337 0.5039 81722 AB.MATG1 14.500 1 1.0603 3.1712 150.00 33.55 0.9759 51.80 0.5117 0.4881 81723 AB.MATG2 14.500 1 1.0603 3.1712 150.00 33.55 0.9759 51.80 0.5117 0.4881 81724 AB.MATV 14.500 1 1.0603 3.1132 150.00 33.55 0.9759 52.33 0.5162 0.4833 81728 PE TAH 33.000 1 1.0455 0.0000 100.00 23.93 0.9725 73.10 0.1761 0.7358 81730 PE TAH NORD 33.000 1 1.0300 0.0000 200.00 5.16 0.9997 75.31 0.0200 0.7767 81827 PV OUARN4 20.000 1 1.0000 0.0000 40.00 -2.08 0.9986 12.84-0.0208 0.4000 81836 PE AKHFENIR 33.000 1 1.0500 0.0000 200.00 56.76 0.9620 101.38 0.2162 0.7619 81921 JORF V 18.000 1 1.1026 2.9359 350.00 210.00 0.8575 62.20 0.7260 0.3869 81922 JORF VI 18.000 1 1.1026 2.9359 350.00 210.00 0.8575 62.20 0.7260 0.3869 81923 JERADA G1 20.000 1 1.0014 1.7176 350.00 -64.48 0.9834 79.93 0.6965 0.5231 81940 PV-MISSOUR M20.000 1 1.0667 0.0000 31.50 0.00 1.0000 17.40 0.0000 0.6712 81944 PE AFTISSAT133.000 1 1.0500 0.0000 100.00 12.90 0.9918 52.68 0.0548 0.4252 81944 PE AFTISSAT133.000 2 1.0500 0.0000 100.00 12.90 0.9918 52.68 0.0548 0.4252 81966 PVLAAYOUNE 22.000 1 1.0300 0.0000 0.00 11.97 0.0000 33.84 0.1162 0.0000 81980 PE MIDLET 33.000 1 1.0200 0.0000 60.00 6.32 0.9945 42.63 0.0553 0.5252 81980 PE MIDLET 33.000 2 1.0200 0.0000 60.00 6.32 0.9945 42.63 0.0553 0.5252 81989 PE AFTISS_EX33.000 1 1.0500 0.0000 200.00 25.69 0.9919 52.79 0.0815 0.6349 81990 PE AMOGHDOUL22.000 1 1.0200 0.0000 60.00 -12.12 0.9802 0.49-0.1748 0.8651 81991 PE BOUJDOUR 33.000 1 1.0438 0.0000 299.99 120.00 0.9285 74.30 0.3285 0.8211 81995 PE KHALLADI 33.000 1 1.0300 0.0000 40.00 -5.38 0.9911 1.09-0.0348 0.2589 81996 PE F.OUED 33.000 1 1.0300 0.0000 40.00 11.56 0.9607 67.95 0.1123 0.3883 81997 PE KOUDIA 33.000 1 1.0000 0.0000 80.00 -25.03 0.9544 3.60-0.1669 0.5333 94000 P.CRUZ 400.00 1 1.0500 1.7745 4692.81 -50.26 0.9999 44.79 0.4792 0.4931 94000 P.CRUZ 400.00 2 1.0500 1.7745 4692.81 -50.26 0.9999 44.79 0.4792 0.4931 94000 P.CRUZ 400.00 3 1.0500 1.7282 4452.73 -47.68 0.9999 43.30 0.4423 0.4796
Network not converged at TIME = -0.002
INITIAL CONDITIONS SUSPECT: I DSTATE(I) STATE(I) MODEL STATE BUS#-SCT X-- NAME --X BASKV ID 2 0.92442E-02 0.53759 GENROU K+1 94000 P.CRUZ 400.00 1 3 0.35815E-01 0.81846 GENROU K+2 94000 P.CRUZ 400.00 1 4 0.16279 0.66433 GENROU K+3 94000 P.CRUZ 400.00 1 8 0.92442E-02 0.53759 GENROU K+1 94000 P.CRUZ 400.00 2 9 0.35815E-01 0.81846 GENROU K+2 94000 P.CRUZ 400.00 2 10 0.16279 0.66433 GENROU K+3 94000 P.CRUZ 400.00 2 14 0.90771E-02 0.52340 GENROU K+1 94000 P.CRUZ 400.00 3 15 0.37185E-01 0.83189 GENROU K+2 94000 P.CRUZ 400.00 3 16 0.15985 0.64667 GENROU K+3 94000 P.CRUZ 400.00 3 170 0.12013E-01 0.36029 GENROU K+1 81201 C.T.M-G3 15.000 1 171 0.17069 1.0002 GENROU K+2 81201 C.T.M-G3 15.000 1 172 0.81409 0.44424 GENROU K+3 81201 C.T.M-G3 15.000 1 173 -0.15032E-01 0.0000 GENROU K+4 81201 C.T.M-G3 15.000 1 176 0.12013E-01 0.36029 GENROU K+1 81202 C.T.M-G4 15.000 1 177 0.17069 1.0002 GENROU K+2 81202 C.T.M-G4 15.000 1 178 0.81409 0.44424 GENROU K+3 81202 C.T.M-G4 15.000 1 179 -0.15032E-01 0.0000 GENROU K+4 81202 C.T.M-G4 15.000 1 206 0.29564E-01 0.43539 GENROU K+1 81212 JORF -G1 22.000 1 207 0.20595 1.0197 GENROU K+2 81212 JORF -G1 22.000 1 208 0.58296 0.54142 GENROU K+3 81212 JORF -G1 22.000 1 212 0.30568E-01 0.43386 GENROU K+1 81213 JORF -G2 22.000 1 213 0.22027 1.0244 GENROU K+2 81213 JORF -G2 22.000 1 214 0.60275 0.54030 GENROU K+3 81213 JORF -G2 22.000 1 215 -0.10152E-01 0.0000 GENROU K+4 81213 JORF -G2 22.000 1 219 0.18224 1.0209 GENROU K+2 81214 JORF -G3 22.000 1 220 0.65618 0.54016 GENROU K+3 81214 JORF -G3 22.000 1 221 -0.10608E-01 0.0000 GENROU K+4 81214 JORF -G3 22.000 1 225 0.19495 1.0257 GENROU K+2 81215 JORF -G4 22.000 1 226 0.67839 0.53890 GENROU K+3 81215 JORF -G4 22.000 1 227 -0.10880E-01 0.0000 GENROU K+4 81215 JORF -G4 22.000 1 306 0.15277E-01 1.1373 GENSAL K 81601 STEPIG1 13.800 1 307 0.31794 1.0360 GENSAL K+1 81601 STEPIG1 13.800 1 308 1.4094 0.44077 GENSAL K+2 81601 STEPIG1 13.800 1 309 -0.33149E-01 0.0000 GENSAL K+3 81601 STEPIG1 13.800 1 311 0.15581E-01 1.1359 GENSAL K 81602 STEPIG2 13.800 1 312 0.32425 1.0344 GENSAL K+1 81602 STEPIG2 13.800 1 313 1.4286 0.44081 GENSAL K+2 81602 STEPIG2 13.800 1 314 -0.33456E-01 0.0000 GENSAL K+3 81602 STEPIG2 13.800 1 316 0.14135E-01 1.1050 GENSAL K 81603 STEPIIG1 10.300 1 317 0.54441 1.0391 GENSAL K+1 81603 STEPIIG1 10.300 1 318 1.0258 0.32595 GENSAL K+2 81603 STEPIIG1 10.300 1 319 -0.45578E-01 0.0000 GENSAL K+3 81603 STEPIIG1 10.300 1 321 0.14082E-01 1.1052 GENSAL K 81604 STEPIIG2 10.300 1 322 0.54236 1.0394 GENSAL K+1 81604 STEPIIG2 10.300 1 323 1.0230 0.32592 GENSAL K+2 81604 STEPIIG2 10.300 1 324 -0.45481E-01 0.0000 GENSAL K+3 81604 STEPIIG2 10.300 1 326 0.15345E-01 0.86681 GENROU K 81605 TAHADG1 21.000 1 327 0.20130E-01 0.45273 GENROU K+1 81605 TAHADG1 21.000 1 328 0.23075 0.80962 GENROU K+2 81605 TAHADG1 21.000 1 329 0.52792 0.68479 GENROU K+3 81605 TAHADG1 21.000 1 330 -0.12934E-01 0.0000 GENROU K+4 81605 TAHADG1 21.000 1 333 0.18003E-01 0.52736 GENROU K+1 81720 C.T.SAFI G1 21.000 1 334 0.83840E-01 0.86001 GENROU K+2 81720 C.T.SAFI G1 21.000 1 335 0.87652 0.65687 GENROU K+3 81720 C.T.SAFI G1 21.000 1 336 -0.11788E-01 0.0000 GENROU K+4 81720 C.T.SAFI G1 21.000 1 339 0.18003E-01 0.52736 GENROU K+1 81721 C.T.SAFI G2 21.000 1 340 0.83840E-01 0.86001 GENROU K+2 81721 C.T.SAFI G2 21.000 1 341 0.87652 0.65687 GENROU K+3 81721 C.T.SAFI G2 21.000 1 342 -0.11788E-01 0.0000 GENROU K+4 81721 C.T.SAFI G2 21.000 1 345 0.13925E-01 0.39716 GENROU K+1 81722 AB.MATG1 14.500 1 346 0.57927E-01 0.96611 GENROU K+2 81722 AB.MATG1 14.500 1 347 0.41738 0.50844 GENROU K+3 81722 AB.MATG1 14.500 1 348 -0.24121E-01 0.0000 GENROU K+4 81722 AB.MATG1 14.500 1 351 0.13925E-01 0.39716 GENROU K+1 81723 AB.MATG2 14.500 1 352 0.57927E-01 0.96611 GENROU K+2 81723 AB.MATG2 14.500 1 353 0.41738 0.50844 GENROU K+3 81723 AB.MATG2 14.500 1 354 -0.24121E-01 0.0000 GENROU K+4 81723 AB.MATG2 14.500 1 357 0.13975E-01 0.40729 GENROU K+1 81724 AB.MATV 14.500 1 358 0.56491E-01 0.96130 GENROU K+2 81724 AB.MATV 14.500 1 359 0.41884 0.51748 GENROU K+3 81724 AB.MATV 14.500 1 360 -0.24120E-01 0.0000 GENROU K+4 81724 AB.MATV 14.500 1 450 0.13125E-01 1.1341 GENROU K 81921 JORF V 18.000 1 451 0.64872E-01 0.40923 GENROU K+1 81921 JORF V 18.000 1 452 0.17182 1.0716 GENROU K+2 81921 JORF V 18.000 1 453 0.65269 0.50017 GENROU K+3 81921 JORF V 18.000 1 454 -0.13230E-01 0.0000 GENROU K+4 81921 JORF V 18.000 1 456 0.13125E-01 1.1341 GENROU K 81922 JORF VI 18.000 1 457 0.64872E-01 0.40923 GENROU K+1 81922 JORF VI 18.000 1 458 0.17182 1.0716 GENROU K+2 81922 JORF VI 18.000 1 459 0.65269 0.50017 GENROU K+3 81922 JORF VI 18.000 1 460 -0.13230E-01 0.0000 GENROU K+4 81922 JORF VI 18.000 1 463 0.29253E-01 0.68193 GENROU K+1 81923 JERADA G1 20.000 1 464 -0.18790E-01 0.55290 GENROU K+2 81923 JERADA G1 20.000 1 465 0.64565 0.81637 GENROU K+3 81923 JERADA G1 20.000 1 466 -0.14017E-01 0.0000 GENROU K+4 81923 JERADA G1 20.000 1 486 0.86064E-01 -0.15835 IEEEST K 81212 JORF -G1 22.000 1 487 0.17213E-01 0.13196E-04 IEEEST K+1 81212 JORF -G1 22.000 1 493 0.88321E-01 -0.15835 IEEEST K 81213 JORF -G2 22.000 1 494 0.17664E-01 0.13196E-04 IEEEST K+1 81213 JORF -G2 22.000 1 500 0.92294E-01 -0.15835 IEEEST K 81214 JORF -G3 22.000 1 501 0.18459E-01 0.13196E-04 IEEEST K+1 81214 JORF -G3 22.000 1 507 0.94652E-01 -0.15835 IEEEST K 81215 JORF -G4 22.000 1 508 0.18930E-01 0.13196E-04 IEEEST K+1 81215 JORF -G4 22.000 1 551 0.32394E-01 0.73170 PSS2A K+3 81722 AB.MATG1 14.500 1 553 0.64788 0.0000 PSS2A K+5 81722 AB.MATG1 14.500 1 567 0.32394E-01 0.73170 PSS2A K+3 81723 AB.MATG2 14.500 1 569 0.64788 0.0000 PSS2A K+5 81723 AB.MATG2 14.500 1 583 0.32394E-01 0.73170 PSS2A K+3 81724 AB.MATV 14.500 1 585 0.64788 0.0000 PSS2A K+5 81724 AB.MATV 14.500 1 628 0.11510 -0.14933 IEEEST K 81921 JORF V 18.000 1 629 0.23020E-01 0.12444E-04 IEEEST K+1 81921 JORF V 18.000 1 635 0.11510 -0.14933 IEEEST K 81922 JORF VI 18.000 1 636 0.23020E-01 0.12444E-04 IEEEST K+1 81922 JORF VI 18.000 1 659 0.22534 1.0500 IEEET1 K 94000 P.CRUZ 400.00 1 663 0.22534 1.0500 IEEET1 K 94000 P.CRUZ 400.00 2 667 0.22534 1.0500 IEEET1 K 94000 P.CRUZ 400.00 3 733 0.68178 1.0195 IEEET1 K 81201 C.T.M-G3 15.000 1 737 0.68178 1.0195 IEEET1 K 81202 C.T.M-G4 15.000 1 757 -0.24872E-02 0.22188E-01 SCRX K 81212 JORF -G1 22.000 1 758 -0.55272 2.4653 SCRX K+1 81212 JORF -G1 22.000 1 759 -0.26084E-02 0.22153E-01 SCRX K 81213 JORF -G2 22.000 1 760 -0.57964 2.4614 SCRX K+1 81213 JORF -G2 22.000 1 761 -0.23222E-02 0.21137E-01 SCRX K 81214 JORF -G3 22.000 1 762 -0.51605 2.3485 SCRX K+1 81214 JORF -G3 22.000 1 763 -0.24353E-02 0.21106E-01 SCRX K 81215 JORF -G4 22.000 1 764 -0.54118 2.3451 SCRX K+1 81215 JORF -G4 22.000 1 809 -0.58956E-02 0.24042E-01 SCRX K 81601 STEPIG1 13.800 1 810 -1.3101 2.6713 SCRX K+1 81601 STEPIG1 13.800 1 811 -0.59981E-02 0.24069E-01 SCRX K 81602 STEPIG2 13.800 1 812 -1.3329 2.6743 SCRX K+1 81602 STEPIG2 13.800 1 813 -0.50302E-02 0.17871E-01 SCRX K 81603 STEPIIG1 10.300 1 814 -1.1178 1.9857 SCRX K+1 81603 STEPIIG1 10.300 1 815 -0.50125E-02 0.17871E-01 SCRX K 81604 STEPIIG2 10.300 1 816 -1.1139 1.9856 SCRX K+1 81604 STEPIIG2 10.300 1 817 0.31590 1.0452 EXST1 K 81605 TAHADG1 21.000 1 819 -0.14973 2.1825 EXST1 K+2 81605 TAHADG1 21.000 1 821 0.79132 1.0588 IEEET1 K 81720 C.T.SAFI G1 21.000 1 825 0.79132 1.0588 IEEET1 K 81721 C.T.SAFI G2 21.000 1 829 0.10204 1.0603 EXST1 K 81722 AB.MATG1 14.500 1 831 -0.48161E-01 3.1712 EXST1 K+2 81722 AB.MATG1 14.500 1 833 0.10204 1.0603 EXST1 K 81723 AB.MATG2 14.500 1 835 -0.48161E-01 3.1712 EXST1 K+2 81723 AB.MATG2 14.500 1 837 0.10204 1.0603 EXST1 K 81724 AB.MATV 14.500 1 839 -0.48161E-01 3.1132 EXST1 K+2 81724 AB.MATV 14.500 1 899 -0.31871E-02 0.23965E-01 SCRX K 81921 JORF V 18.000 1 900 -0.70824 2.6628 SCRX K+1 81921 JORF V 18.000 1 901 -0.31871E-02 0.23965E-01 SCRX K 81922 JORF VI 18.000 1 902 -0.70824 2.6628 SCRX K+1 81922 JORF VI 18.000 1 903 0.52900 1.0014 IEEET1 K 81923 JERADA G1 20.000 1 1249 6.0660 1.0500 REGCA1 K+2 81989 PE AFTISSEX33.000 1 1252 6.8049 1.0200 REGCA1 K+2 81980 PE MIDLET 33.000 1 1255 6.8049 1.0200 REGCA1 K+2 81980 PE MIDLET 33.000 2 1262 5.0557 1.1045 REGCA1 K+2 81250 PE OUALIDIA 33.000 1 1266 -0.94768 0.98131E-01 WT3G1 K+3 81266 PE TANGER 33.000 1 1269 -38.846 1.0667 REGCA1 K+2 81390 PV ZAGORA 60.000 1 1273 -1.7161 1.3144 WT3G1 K+3 81730 PE TAH NORD 33.000 1 1277 -1.6920 1.2758 WT3G1 K+3 81728 PE TAH 33.000 1 1280 -0.23876E-01 0.0000 WT3G2 K+2 81836 PE AKHFENIR 33.000 1 1281 -0.75010 1.7695 WT3G2 K+3 81836 PE AKHFENIR 33.000 1 1282 4.1212 1.0500 WT3G2 K+4 81836 PE AKHFENIR 33.000 1 1285 4.0081 1.0667 REGCA1 K+2 81940 PV-MISSOUR M20.000 1 1288 5.2972 1.0500 REGCA1 K+2 81944 PE AFTISSAT133.000 1 1291 5.2972 1.0500 REGCA1 K+2 81944 PE AFTISSAT133.000 2 1294 7.8303 1.0300 REGCA1 K+2 81966 PVLAAYOUNE 22.000 1 1295 -29.330 0.82112 WT3G1 K 81991 PE BOUJDOUR 33.000 1 1298 -2.2097 1.2969 WT3G1 K+3 81991 PE BOUJDOUR 33.000 1 1302 -7.2500 0.84843E-02 WT3G1 K+3 81990 PE AMOGHDOUL22.000 1 1306 -1.1717 0.19002E-01 WT3G1 K+3 81995 PE KHALLADI 33.000 1 1310 -1.4741 1.1859 WT3G1 K+3 81996 PE F.OUED 33.000 1 1314 -6.4147 0.22401 WT3G1 K+3 81827 PV OUARN4 20.000 1 1318 -1.6721 0.62780E-01 WT3G1 K+3 81997 PE KOUDIA 33.000 1 1319 6.0660 1.0500 REECB1 K 81989 PE AFTISSEX33.000 1 1321 0.26143E-01 1.0500 REECB1 K+2 81989 PE AFTISSEX33.000 1 1325 6.8049 1.0200 REECB1 K 81980 PE MIDLET 33.000 1 1327 0.40712E-01 1.0200 REECB1 K+2 81980 PE MIDLET 33.000 1 1331 6.8049 1.0200 REECB1 K 81980 PE MIDLET 33.000 2 1333 0.40712E-01 1.0200 REECB1 K+2 81980 PE MIDLET 33.000 2 1351 -0.28792 0.68658E-01 REECA1 K+4 81250 PE OUALIDIA 33.000 1 1357 3.3578 1.0408 WT3E1 K+4 81266 PE TANGER 33.000 1 1360 -5.6652 1.1410 WT3E1 K+7 81266 PE TANGER 33.000 1 1363 -38.846 1.0667 REECB1 K 81390 PV ZAGORA 60.000 1 1373 2.0771 1.0300 WT3E1 K+4 81730 PE TAH NORD 33.000 1 1376 -4.1541 1.0460 WT3E1 K+7 81730 PE TAH NORD 33.000 1 1383 2.2184 1.0455 WT3E1 K+4 81728 PE TAH 33.000 1 1386 -4.4368 1.1863 WT3E1 K+7 81728 PE TAH 33.000 1 1393 4.1212 1.0500 WT3E1 K+4 81836 PE AKHFENIR 33.000 1 1396 -3.2970 1.2230 WT3E1 K+7 81836 PE AKHFENIR 33.000 1 1399 4.0081 1.0667 REECB1 K 81940 PV-MISSOUR M20.000 1 1401 0.33168E-01 1.0667 REECB1 K+2 81940 PV-MISSOUR M20.000 1 1405 5.2972 1.0500 REECB1 K 81944 PE AFTISSAT133.000 1 1407 0.25042E-01 1.0500 REECB1 K+2 81944 PE AFTISSAT133.000 1 1411 5.2972 1.0500 REECB1 K 81944 PE AFTISSAT133.000 2 1413 0.25042E-01 1.0500 REECB1 K+2 81944 PE AFTISSAT133.000 2 1417 7.8303 1.0300 REECB1 K 81966 PVLAAYOUNE 22.000 1 1423 -0.22575 0.34286 WT3E1 K 81991 PE BOUJDOUR 33.000 1 1427 6.6736 1.0438 WT3E1 K+4 81991 PE BOUJDOUR 33.000 1 1430 -13.347 1.0865 WT3E1 K+7 81991 PE BOUJDOUR 33.000 1 1437 20.970 1.0200 WT3E1 K+4 81990 PE AMOGHDOUL22.000 1 1447 14.911 1.0300 WT3E1 K+4 81995 PE KHALLADI 33.000 1 1457 2.4415 1.0300 WT3E1 K+4 81996 PE F.OUED 33.000 1 1460 -0.12208E-01 1.1198 WT3E1 K+7 81996 PE F.OUED 33.000 1 1463 75.600 1.0000 REECB1 K 81827 PV OUARN4 20.000 1 1473 20.108 1.0000 WT3E1 K+4 81997 PE KOUDIA 33.000 1 1481 -0.88620E-01 0.0000 WT12T1 K+2 81989 PE AFTISSEX33.000 1 1489 -0.11275 0.0000 WTDTA1 K+2 81250 PE OUALIDIA 33.000 1 1548 6.0000 0.0000 WT3P1 K+2 81991 PE BOUJDOUR 33.000 1 1563 3.6133 0.0000 WT3P1 K+2 81997 PE KOUDIA 33.000 1 1564 0.77028 0.66666 WT12A1 K 81989 PE AFTISSEX33.000 1 1568 6.0660 1.0500 REPCA1 K 81989 PE AFTISSEX33.000 1 1572 3.8514 0.66666 REPCA1 K+4 81989 PE AFTISSEX33.000 1 1575 6.8049 1.0200 REPCA1 K 81980 PE MIDLET 33.000 1 1579 3.5740 0.53571 REPCA1 K+4 81980 PE MIDLET 33.000 1 1582 6.8049 1.0200 REPCA1 K 81980 PE MIDLET 33.000 2 1586 3.5740 0.53571 REPCA1 K+4 81980 PE MIDLET 33.000 2 1589 0.95895 1.0400 REPCA1 K 81250 PE OUALIDIA 33.000 1 1596 -38.846 1.0667 REPCA1 K 81390 PV ZAGORA 60.000 1 1600 -35.526 0.71053 REPCA1 K+4 81390 PV ZAGORA 60.000 1 1603 4.0081 1.0667 REPCA1 K 81940 PV-MISSOUR M20.000 1 1607 2.6901 0.71591 REPCA1 K+4 81940 PV-MISSOUR M20.000 1 1610 5.2972 1.0500 REPCA1 K 81944 PE AFTISSAT133.000 1 1614 2.2522 0.44643 REPCA1 K+4 81944 PE AFTISSAT133.000 1 1617 5.2972 1.0500 REPCA1 K 81944 PE AFTISSAT133.000 2 1621 2.2522 0.44643 REPCA1 K+4 81944 PE AFTISSAT133.000 2 1624 7.8303 1.0300 REPCA1 K 81966 PVLAAYOUNE 22.000 1 1631 75.600 1.0000 REPCA1 K 81827 PV OUAR_N4 20.000 1
Channel output file is "Hope2.out"
Channel output file is "Hope2.out"
Network not converged at TIME = -0.002
Network not converged at TIME = -0.001
Network not converged at TIME = 0.0
Network not converged at TIME = 0.001
Network not converged at TIME = 0.002
Network not converged at TIME = 0.003
Network not converged at TIME = 0.004
Network not converged at TIME = 0.005
Network not converged at TIME = 0.006
Network not converged at TIME = 0.007
Network not converged at TIME = 0.008
Network not converged at TIME = 0.009
Network not converged at TIME = 0.01
Network not converged at TIME = 0.011
Network not converged at TIME = 0.012
Network not converged at TIME = 0.013
Network not converged at TIME = 0.014
Network not converged at TIME = 0.015
Network not converged at TIME = 0.016
Network not converged at TIME = 0.017
Network not converged at TIME = 0.018
Network not converged at TIME = 0.019
Network not converged at TIME = 0.02
Network not converged at TIME = 0.021
Network not converged at TIME = 0.022
Network not converged at TIME = 0.023
Network not converged at TIME = 0.024
Network not converged at TIME = 0.025
Network not converged at TIME = 0.026
Network not converged at TIME = 0.027
Network not converged at TIME = 0.028
Network not converged at TIME = 0.029
Network not converged at TIME = 0.03
Network not converged at TIME = 0.031
Network not converged at TIME = 0.032
Network not converged at TIME = 0.033
Network not converged at TIME = 0.034
Network not converged at TIME = 0.035
Network not converged at TIME = 0.036
Network not converged at TIME = 0.037
Network not converged at TIME = 0.038
Network not converged at TIME = 0.039
Network not converged at TIME = 0.04
Network not converged at TIME = 0.041
Network not converged at TIME = 0.042
Network not converged at TIME = 0.043
Network not converged at TIME = 0.044
Network not converged at TIME = 0.045
Network not converged at TIME = 0.046
Network not converged at TIME = 0.047
Network not converged at TIME = 0.048
Network not converged at TIME = 0.049
| 2 | No.2 Revision |
I run a load flow for a case , it converges normally. When I try STRT and initializing the dynamic simulation , it does not converge as follows: '' NITIAL CONDITION LOAD FLOW USED 1 ITERATIONS
----------------------------- MACHINE INITIAL CONDITIONS ----------------------------- BUS#-SCT X-- NAME --X BASKV ID ETERM EFD POWER VARS P.F. ANGLE ID IQ 81201 C.T.M-G3 15.000 1 1.0195 2.3545 120.00 90.00 0.8000 38.31 0.7174 0.3229 81202 C.T.M-G4 15.000 1 1.0195 2.3545 120.00 90.00 0.8000 38.31 0.7174 0.3229 81212 JORF -G1 22.000 1 1.0825 2.6688 320.00 150.00 0.9055 57.59 0.7277 0.4224 81213 JORF -G2 22.000 1 1.0867 2.6748 320.00 149.51 0.9060 58.30 0.7224 0.4241 81214 JORF -G3 22.000 1 1.0825 2.5424 320.00 150.00 0.9055 57.54 0.7273 0.4230 81215 JORF -G4 22.000 1 1.0867 2.5484 320.00 149.51 0.9060 58.24 0.7220 0.4247 81250 PE OUALIDIA 33.000 1 1.1045 0.0000 32.00 2.71 0.9964 54.08 0.0687 0.8118 81266 PE TANGER 33.000 1 1.0500 0.0000 140.00 19.11 0.9908 5.62 0.1138 0.8333 81390 PV ZAGORA 60.000 1 1.0667 0.0000 27.00 -3.96 0.9894 19.60-0.0978 0.6661 81601 STEPIG1 13.800 1 1.0733 2.8671 160.00 80.00 0.8944 46.15 0.7240 0.4740 81602 STEPIG2 13.800 1 1.0717 2.8662 160.00 80.00 0.8944 45.98 0.7255 0.4740 81603 STEPIIG1 10.300 1 1.0657 2.1161 60.00 26.00 0.9175 37.98 0.4388 0.4289 81604 STEPIIG2 10.300 1 1.0659 2.1164 60.00 26.00 0.9175 38.00 0.4387 0.4288 81605 TAHADG1 21.000 1 1.0452 2.1825 380.00 38.31 0.9950 53.79 0.5719 0.4550 81720 C.T.SAFI G1 21.000 1 1.0588 2.1105 650.00 86.97 0.9912 85.26 0.6337 0.5039 81721 C.T.SAFI G2 21.000 1 1.0588 2.1105 650.00 86.97 0.9912 85.26 0.6337 0.5039 81722 AB.MATG1 14.500 1 1.0603 3.1712 150.00 33.55 0.9759 51.80 0.5117 0.4881 81723 AB.MATG2 14.500 1 1.0603 3.1712 150.00 33.55 0.9759 51.80 0.5117 0.4881 81724 AB.MATV 14.500 1 1.0603 3.1132 150.00 33.55 0.9759 52.33 0.5162 0.4833 81728 PE TAH 33.000 1 1.0455 0.0000 100.00 23.93 0.9725 73.10 0.1761 0.7358 81730 PE TAH NORD 33.000 1 1.0300 0.0000 200.00 5.16 0.9997 75.31 0.0200 0.7767 81827 PV OUARN4 20.000 1 1.0000 0.0000 40.00 -2.08 0.9986 12.84-0.0208 0.4000 81836 PE AKHFENIR 33.000 1 1.0500 0.0000 200.00 56.76 0.9620 101.38 0.2162 0.7619 81921 JORF V 18.000 1 1.1026 2.9359 350.00 210.00 0.8575 62.20 0.7260 0.3869 81922 JORF VI 18.000 1 1.1026 2.9359 350.00 210.00 0.8575 62.20 0.7260 0.3869 81923 JERADA G1 20.000 1 1.0014 1.7176 350.00 -64.48 0.9834 79.93 0.6965 0.5231 81940 PV-MISSOUR M20.000 1 1.0667 0.0000 31.50 0.00 1.0000 17.40 0.0000 0.6712 81944 PE AFTISSAT133.000 1 1.0500 0.0000 100.00 12.90 0.9918 52.68 0.0548 0.4252 81944 PE AFTISSAT133.000 2 1.0500 0.0000 100.00 12.90 0.9918 52.68 0.0548 0.4252 81966 PVLAAYOUNE 22.000 1 1.0300 0.0000 0.00 11.97 0.0000 33.84 0.1162 0.0000 81980 PE MIDLET 33.000 1 1.0200 0.0000 60.00 6.32 0.9945 42.63 0.0553 0.5252 81980 PE MIDLET 33.000 2 1.0200 0.0000 60.00 6.32 0.9945 42.63 0.0553 0.5252 81989 PE AFTISS_EX33.000 1 1.0500 0.0000 200.00 25.69 0.9919 52.79 0.0815 0.6349 81990 PE AMOGHDOUL22.000 1 1.0200 0.0000 60.00 -12.12 0.9802 0.49-0.1748 0.8651 81991 PE BOUJDOUR 33.000 1 1.0438 0.0000 299.99 120.00 0.9285 74.30 0.3285 0.8211 81995 PE KHALLADI 33.000 1 1.0300 0.0000 40.00 -5.38 0.9911 1.09-0.0348 0.2589 81996 PE F.OUED 33.000 1 1.0300 0.0000 40.00 11.56 0.9607 67.95 0.1123 0.3883 81997 PE KOUDIA 33.000 1 1.0000 0.0000 80.00 -25.03 0.9544 3.60-0.1669 0.5333 94000 P.CRUZ 400.00 1 1.0500 1.7745 4692.81 -50.26 0.9999 44.79 0.4792 0.4931 94000 P.CRUZ 400.00 2 1.0500 1.7745 4692.81 -50.26 0.9999 44.79 0.4792 0.4931 94000 P.CRUZ 400.00 3 1.0500 1.7282 4452.73 -47.68 0.9999 43.30 0.4423 0.4796
Network not converged at TIME = -0.002
INITIAL CONDITIONS SUSPECT: I DSTATE(I) STATE(I) MODEL STATE BUS#-SCT X-- NAME --X BASKV ID 2 0.92442E-02 0.53759 GENROU K+1 94000 P.CRUZ 400.00 1 3 0.35815E-01 0.81846 GENROU K+2 94000 P.CRUZ 400.00 1 4 0.16279 0.66433 GENROU K+3 94000 P.CRUZ 400.00 1 8 0.92442E-02 0.53759 GENROU K+1 94000 P.CRUZ 400.00 2 9 0.35815E-01 0.81846 GENROU K+2 94000 P.CRUZ 400.00 2 10 0.16279 0.66433 GENROU K+3 94000 P.CRUZ 400.00 2 14 0.90771E-02 0.52340 GENROU K+1 94000 P.CRUZ 400.00 3 15 0.37185E-01 0.83189 GENROU K+2 94000 P.CRUZ 400.00 3 16 0.15985 0.64667 GENROU K+3 94000 P.CRUZ 400.00 3 170 0.12013E-01 0.36029 GENROU K+1 81201 C.T.M-G3 15.000 1 171 0.17069 1.0002 GENROU K+2 81201 C.T.M-G3 15.000 1 172 0.81409 0.44424 GENROU K+3 81201 C.T.M-G3 15.000 1 173 -0.15032E-01 0.0000 GENROU K+4 81201 C.T.M-G3 15.000 1 176 0.12013E-01 0.36029 GENROU K+1 81202 C.T.M-G4 15.000 1 177 0.17069 1.0002 GENROU K+2 81202 C.T.M-G4 15.000 1 178 0.81409 0.44424 GENROU K+3 81202 C.T.M-G4 15.000 1 179 -0.15032E-01 0.0000 GENROU K+4 81202 C.T.M-G4 15.000 1 206 0.29564E-01 0.43539 GENROU K+1 81212 JORF -G1 22.000 1 207 0.20595 1.0197 GENROU K+2 81212 JORF -G1 22.000 1 208 0.58296 0.54142 GENROU K+3 81212 JORF -G1 22.000 1 212 0.30568E-01 0.43386 GENROU K+1 81213 JORF -G2 22.000 1 213 0.22027 1.0244 GENROU K+2 81213 JORF -G2 22.000 1 214 0.60275 0.54030 GENROU K+3 81213 JORF -G2 22.000 1 215 -0.10152E-01 0.0000 GENROU K+4 81213 JORF -G2 22.000 1 219 0.18224 1.0209 GENROU K+2 81214 JORF -G3 22.000 1 220 0.65618 0.54016 GENROU K+3 81214 JORF -G3 22.000 1 221 -0.10608E-01 0.0000 GENROU K+4 81214 JORF -G3 22.000 1 225 0.19495 1.0257 GENROU K+2 81215 JORF -G4 22.000 1 226 0.67839 0.53890 GENROU K+3 81215 JORF -G4 22.000 1 227 -0.10880E-01 0.0000 GENROU K+4 81215 JORF -G4 22.000 1 306 0.15277E-01 1.1373 GENSAL K 81601 STEPIG1 13.800 1 307 0.31794 1.0360 GENSAL K+1 81601 STEPIG1 13.800 1 308 1.4094 0.44077 GENSAL K+2 81601 STEPIG1 13.800 1 309 -0.33149E-01 0.0000 GENSAL K+3 81601 STEPIG1 13.800 1 311 0.15581E-01 1.1359 GENSAL K 81602 STEPIG2 13.800 1 312 0.32425 1.0344 GENSAL K+1 81602 STEPIG2 13.800 1 313 1.4286 0.44081 GENSAL K+2 81602 STEPIG2 13.800 1 314 -0.33456E-01 0.0000 GENSAL K+3 81602 STEPIG2 13.800 1 316 0.14135E-01 1.1050 GENSAL K 81603 STEPIIG1 10.300 1 317 0.54441 1.0391 GENSAL K+1 81603 STEPIIG1 10.300 1 318 1.0258 0.32595 GENSAL K+2 81603 STEPIIG1 10.300 1 319 -0.45578E-01 0.0000 GENSAL K+3 81603 STEPIIG1 10.300 1 321 0.14082E-01 1.1052 GENSAL K 81604 STEPIIG2 10.300 1 322 0.54236 1.0394 GENSAL K+1 81604 STEPIIG2 10.300 1 323 1.0230 0.32592 GENSAL K+2 81604 STEPIIG2 10.300 1 324 -0.45481E-01 0.0000 GENSAL K+3 81604 STEPIIG2 10.300 1 326 0.15345E-01 0.86681 GENROU K 81605 TAHADG1 21.000 1 327 0.20130E-01 0.45273 GENROU K+1 81605 TAHADG1 21.000 1 328 0.23075 0.80962 GENROU K+2 81605 TAHADG1 21.000 1 329 0.52792 0.68479 GENROU K+3 81605 TAHADG1 21.000 1 330 -0.12934E-01 0.0000 GENROU K+4 81605 TAHADG1 21.000 1 333 0.18003E-01 0.52736 GENROU K+1 81720 C.T.SAFI G1 21.000 1 334 0.83840E-01 0.86001 GENROU K+2 81720 C.T.SAFI G1 21.000 1 335 0.87652 0.65687 GENROU K+3 81720 C.T.SAFI G1 21.000 1 336 -0.11788E-01 0.0000 GENROU K+4 81720 C.T.SAFI G1 21.000 1 339 0.18003E-01 0.52736 GENROU K+1 81721 C.T.SAFI G2 21.000 1 340 0.83840E-01 0.86001 GENROU K+2 81721 C.T.SAFI G2 21.000 1 341 0.87652 0.65687 GENROU K+3 81721 C.T.SAFI G2 21.000 1 342 -0.11788E-01 0.0000 GENROU K+4 81721 C.T.SAFI G2 21.000 1 345 0.13925E-01 0.39716 GENROU K+1 81722 AB.MATG1 14.500 1 346 0.57927E-01 0.96611 GENROU K+2 81722 AB.MATG1 14.500 1 347 0.41738 0.50844 GENROU K+3 81722 AB.MATG1 14.500 1 348 -0.24121E-01 0.0000 GENROU K+4 81722 AB.MATG1 14.500 1 351 0.13925E-01 0.39716 GENROU K+1 81723 AB.MATG2 14.500 1 352 0.57927E-01 0.96611 GENROU K+2 81723 AB.MATG2 14.500 1 353 0.41738 0.50844 GENROU K+3 81723 AB.MATG2 14.500 1 354 -0.24121E-01 0.0000 GENROU K+4 81723 AB.MATG2 14.500 1 357 0.13975E-01 0.40729 GENROU K+1 81724 AB.MATV 14.500 1 358 0.56491E-01 0.96130 GENROU K+2 81724 AB.MATV 14.500 1 359 0.41884 0.51748 GENROU K+3 81724 AB.MATV 14.500 1 360 -0.24120E-01 0.0000 GENROU K+4 81724 AB.MATV 14.500 1 450 0.13125E-01 1.1341 GENROU K 81921 JORF V 18.000 1 451 0.64872E-01 0.40923 GENROU K+1 81921 JORF V 18.000 1 452 0.17182 1.0716 GENROU K+2 81921 JORF V 18.000 1 453 0.65269 0.50017 GENROU K+3 81921 JORF V 18.000 1 454 -0.13230E-01 0.0000 GENROU K+4 81921 JORF V 18.000 1 456 0.13125E-01 1.1341 GENROU K 81922 JORF VI 18.000 1 457 0.64872E-01 0.40923 GENROU K+1 81922 JORF VI 18.000 1 458 0.17182 1.0716 GENROU K+2 81922 JORF VI 18.000 1 459 0.65269 0.50017 GENROU K+3 81922 JORF VI 18.000 1 460 -0.13230E-01 0.0000 GENROU K+4 81922 JORF VI 18.000 1 463 0.29253E-01 0.68193 GENROU K+1 81923 JERADA G1 20.000 1 464 -0.18790E-01 0.55290 GENROU K+2 81923 JERADA G1 20.000 1 465 0.64565 0.81637 GENROU K+3 81923 JERADA G1 20.000 1 466 -0.14017E-01 0.0000 GENROU K+4 81923 JERADA G1 20.000 1 486 0.86064E-01 -0.15835 IEEEST K 81212 JORF -G1 22.000 1 487 0.17213E-01 0.13196E-04 IEEEST K+1 81212 JORF -G1 22.000 1 493 0.88321E-01 -0.15835 IEEEST K 81213 JORF -G2 22.000 1 494 0.17664E-01 0.13196E-04 IEEEST K+1 81213 JORF -G2 22.000 1 500 0.92294E-01 -0.15835 IEEEST K 81214 JORF -G3 22.000 1 501 0.18459E-01 0.13196E-04 IEEEST K+1 81214 JORF -G3 22.000 1 507 0.94652E-01 -0.15835 IEEEST K 81215 JORF -G4 22.000 1 508 0.18930E-01 0.13196E-04 IEEEST K+1 81215 JORF -G4 22.000 1 551 0.32394E-01 0.73170 PSS2A K+3 81722 AB.MATG1 14.500 1 553 0.64788 0.0000 PSS2A K+5 81722 AB.MATG1 14.500 1 567 0.32394E-01 0.73170 PSS2A K+3 81723 AB.MATG2 14.500 1 569 0.64788 0.0000 PSS2A K+5 81723 AB.MATG2 14.500 1 583 0.32394E-01 0.73170 PSS2A K+3 81724 AB.MATV 14.500 1 585 0.64788 0.0000 PSS2A K+5 81724 AB.MATV 14.500 1 628 0.11510 -0.14933 IEEEST K 81921 JORF V 18.000 1 629 0.23020E-01 0.12444E-04 IEEEST K+1 81921 JORF V 18.000 1 635 0.11510 -0.14933 IEEEST K 81922 JORF VI 18.000 1 636 0.23020E-01 0.12444E-04 IEEEST K+1 81922 JORF VI 18.000 1 659 0.22534 1.0500 IEEET1 K 94000 P.CRUZ 400.00 1 663 0.22534 1.0500 IEEET1 K 94000 P.CRUZ 400.00 2 667 0.22534 1.0500 IEEET1 K 94000 P.CRUZ 400.00 3 733 0.68178 1.0195 IEEET1 K 81201 C.T.M-G3 15.000 1 737 0.68178 1.0195 IEEET1 K 81202 C.T.M-G4 15.000 1 757 -0.24872E-02 0.22188E-01 SCRX K 81212 JORF -G1 22.000 1 758 -0.55272 2.4653 SCRX K+1 81212 JORF -G1 22.000 1 759 -0.26084E-02 0.22153E-01 SCRX K 81213 JORF -G2 22.000 1 760 -0.57964 2.4614 SCRX K+1 81213 JORF -G2 22.000 1 761 -0.23222E-02 0.21137E-01 SCRX K 81214 JORF -G3 22.000 1 762 -0.51605 2.3485 SCRX K+1 81214 JORF -G3 22.000 1 763 -0.24353E-02 0.21106E-01 SCRX K 81215 JORF -G4 22.000 1 764 -0.54118 2.3451 SCRX K+1 81215 JORF -G4 22.000 1 809 -0.58956E-02 0.24042E-01 SCRX K 81601 STEPIG1 13.800 1 810 -1.3101 2.6713 SCRX K+1 81601 STEPIG1 13.800 1 811 -0.59981E-02 0.24069E-01 SCRX K 81602 STEPIG2 13.800 1 812 -1.3329 2.6743 SCRX K+1 81602 STEPIG2 13.800 1 813 -0.50302E-02 0.17871E-01 SCRX K 81603 STEPIIG1 10.300 1 814 -1.1178 1.9857 SCRX K+1 81603 STEPIIG1 10.300 1 815 -0.50125E-02 0.17871E-01 SCRX K 81604 STEPIIG2 10.300 1 816 -1.1139 1.9856 SCRX K+1 81604 STEPIIG2 10.300 1 817 0.31590 1.0452 EXST1 K 81605 TAHADG1 21.000 1 819 -0.14973 2.1825 EXST1 K+2 81605 TAHADG1 21.000 1 821 0.79132 1.0588 IEEET1 K 81720 C.T.SAFI G1 21.000 1 825 0.79132 1.0588 IEEET1 K 81721 C.T.SAFI G2 21.000 1 829 0.10204 1.0603 EXST1 K 81722 AB.MATG1 14.500 1 831 -0.48161E-01 3.1712 EXST1 K+2 81722 AB.MATG1 14.500 1 833 0.10204 1.0603 EXST1 K 81723 AB.MATG2 14.500 1 835 -0.48161E-01 3.1712 EXST1 K+2 81723 AB.MATG2 14.500 1 837 0.10204 1.0603 EXST1 K 81724 AB.MATV 14.500 1 839 -0.48161E-01 3.1132 EXST1 K+2 81724 AB.MATV 14.500 1 899 -0.31871E-02 0.23965E-01 SCRX K 81921 JORF V 18.000 1 900 -0.70824 2.6628 SCRX K+1 81921 JORF V 18.000 1 901 -0.31871E-02 0.23965E-01 SCRX K 81922 JORF VI 18.000 1 902 -0.70824 2.6628 SCRX K+1 81922 JORF VI 18.000 1 903 0.52900 1.0014 IEEET1 K 81923 JERADA G1 20.000 1 1249 6.0660 1.0500 REGCA1 K+2 81989 PE AFTISSEX33.000 1 1252 6.8049 1.0200 REGCA1 K+2 81980 PE MIDLET 33.000 1 1255 6.8049 1.0200 REGCA1 K+2 81980 PE MIDLET 33.000 2 1262 5.0557 1.1045 REGCA1 K+2 81250 PE OUALIDIA 33.000 1 1266 -0.94768 0.98131E-01 WT3G1 K+3 81266 PE TANGER 33.000 1 1269 -38.846 1.0667 REGCA1 K+2 81390 PV ZAGORA 60.000 1 1273 -1.7161 1.3144 WT3G1 K+3 81730 PE TAH NORD 33.000 1 1277 -1.6920 1.2758 WT3G1 K+3 81728 PE TAH 33.000 1 1280 -0.23876E-01 0.0000 WT3G2 K+2 81836 PE AKHFENIR 33.000 1 1281 -0.75010 1.7695 WT3G2 K+3 81836 PE AKHFENIR 33.000 1 1282 4.1212 1.0500 WT3G2 K+4 81836 PE AKHFENIR 33.000 1 1285 4.0081 1.0667 REGCA1 K+2 81940 PV-MISSOUR M20.000 1 1288 5.2972 1.0500 REGCA1 K+2 81944 PE AFTISSAT133.000 1 1291 5.2972 1.0500 REGCA1 K+2 81944 PE AFTISSAT133.000 2 1294 7.8303 1.0300 REGCA1 K+2 81966 PVLAAYOUNE 22.000 1 1295 -29.330 0.82112 WT3G1 K 81991 PE BOUJDOUR 33.000 1 1298 -2.2097 1.2969 WT3G1 K+3 81991 PE BOUJDOUR 33.000 1 1302 -7.2500 0.84843E-02 WT3G1 K+3 81990 PE AMOGHDOUL22.000 1 1306 -1.1717 0.19002E-01 WT3G1 K+3 81995 PE KHALLADI 33.000 1 1310 -1.4741 1.1859 WT3G1 K+3 81996 PE F.OUED 33.000 1 1314 -6.4147 0.22401 WT3G1 K+3 81827 PV OUARN4 20.000 1 1318 -1.6721 0.62780E-01 WT3G1 K+3 81997 PE KOUDIA 33.000 1 1319 6.0660 1.0500 REECB1 K 81989 PE AFTISSEX33.000 1 1321 0.26143E-01 1.0500 REECB1 K+2 81989 PE AFTISSEX33.000 1 1325 6.8049 1.0200 REECB1 K 81980 PE MIDLET 33.000 1 1327 0.40712E-01 1.0200 REECB1 K+2 81980 PE MIDLET 33.000 1 1331 6.8049 1.0200 REECB1 K 81980 PE MIDLET 33.000 2 1333 0.40712E-01 1.0200 REECB1 K+2 81980 PE MIDLET 33.000 2 1351 -0.28792 0.68658E-01 REECA1 K+4 81250 PE OUALIDIA 33.000 1 1357 3.3578 1.0408 WT3E1 K+4 81266 PE TANGER 33.000 1 1360 -5.6652 1.1410 WT3E1 K+7 81266 PE TANGER 33.000 1 1363 -38.846 1.0667 REECB1 K 81390 PV ZAGORA 60.000 1 1373 2.0771 1.0300 WT3E1 K+4 81730 PE TAH NORD 33.000 1 1376 -4.1541 1.0460 WT3E1 K+7 81730 PE TAH NORD 33.000 1 1383 2.2184 1.0455 WT3E1 K+4 81728 PE TAH 33.000 1 1386 -4.4368 1.1863 WT3E1 K+7 81728 PE TAH 33.000 1 1393 4.1212 1.0500 WT3E1 K+4 81836 PE AKHFENIR 33.000 1 1396 -3.2970 1.2230 WT3E1 K+7 81836 PE AKHFENIR 33.000 1 1399 4.0081 1.0667 REECB1 K 81940 PV-MISSOUR M20.000 1 1401 0.33168E-01 1.0667 REECB1 K+2 81940 PV-MISSOUR M20.000 1 1405 5.2972 1.0500 REECB1 K 81944 PE AFTISSAT133.000 1 1407 0.25042E-01 1.0500 REECB1 K+2 81944 PE AFTISSAT133.000 1 1411 5.2972 1.0500 REECB1 K 81944 PE AFTISSAT133.000 2 1413 0.25042E-01 1.0500 REECB1 K+2 81944 PE AFTISSAT133.000 2 1417 7.8303 1.0300 REECB1 K 81966 PVLAAYOUNE 22.000 1 1423 -0.22575 0.34286 WT3E1 K 81991 PE BOUJDOUR 33.000 1 1427 6.6736 1.0438 WT3E1 K+4 81991 PE BOUJDOUR 33.000 1 1430 -13.347 1.0865 WT3E1 K+7 81991 PE BOUJDOUR 33.000 1 1437 20.970 1.0200 WT3E1 K+4 81990 PE AMOGHDOUL22.000 1 1447 14.911 1.0300 WT3E1 K+4 81995 PE KHALLADI 33.000 1 1457 2.4415 1.0300 WT3E1 K+4 81996 PE F.OUED 33.000 1 1460 -0.12208E-01 1.1198 WT3E1 K+7 81996 PE F.OUED 33.000 1 1463 75.600 1.0000 REECB1 K 81827 PV OUARN4 20.000 1 1473 20.108 1.0000 WT3E1 K+4 81997 PE KOUDIA 33.000 1 1481 -0.88620E-01 0.0000 WT12T1 K+2 81989 PE AFTISSEX33.000 1 1489 -0.11275 0.0000 WTDTA1 K+2 81250 PE OUALIDIA 33.000 1 1548 6.0000 0.0000 WT3P1 K+2 81991 PE BOUJDOUR 33.000 1 1563 3.6133 0.0000 WT3P1 K+2 81997 PE KOUDIA 33.000 1 1564 0.77028 0.66666 WT12A1 K 81989 PE AFTISSEX33.000 1 1568 6.0660 1.0500 REPCA1 K 81989 PE AFTISSEX33.000 1 1572 3.8514 0.66666 REPCA1 K+4 81989 PE AFTISSEX33.000 1 1575 6.8049 1.0200 REPCA1 K 81980 PE MIDLET 33.000 1 1579 3.5740 0.53571 REPCA1 K+4 81980 PE MIDLET 33.000 1 1582 6.8049 1.0200 REPCA1 K 81980 PE MIDLET 33.000 2 1586 3.5740 0.53571 REPCA1 K+4 81980 PE MIDLET 33.000 2 1589 0.95895 1.0400 REPCA1 K 81250 PE OUALIDIA 33.000 1 1596 -38.846 1.0667 REPCA1 K 81390 PV ZAGORA 60.000 1 1600 -35.526 0.71053 REPCA1 K+4 81390 PV ZAGORA 60.000 1 1603 4.0081 1.0667 REPCA1 K 81940 PV-MISSOUR M20.000 1 1607 2.6901 0.71591 REPCA1 K+4 81940 PV-MISSOUR M20.000 1 1610 5.2972 1.0500 REPCA1 K 81944 PE AFTISSAT133.000 1 1614 2.2522 0.44643 REPCA1 K+4 81944 PE AFTISSAT133.000 1 1617 5.2972 1.0500 REPCA1 K 81944 PE AFTISSAT133.000 2 1621 2.2522 0.44643 REPCA1 K+4 81944 PE AFTISSAT133.000 2 1624 7.8303 1.0300 REPCA1 K 81966 PVLAAYOUNE 22.000 1 1631 75.600 1.0000 REPCA1 K 81827 PV OUAR_N4 20.000 1
Channel output file is "Hope2.out"
Channel output file is "Hope2.out"
Network not converged at TIME = -0.002
Network not converged at TIME = -0.001
Network not converged at TIME = 0.0
Network not converged at TIME = 0.001
Network not converged at TIME = 0.002
Network not converged at TIME = 0.003
Network not converged at TIME = 0.004
Network not converged at TIME = 0.005
Network not converged at TIME = 0.006
Network not converged at TIME = 0.007
Network not converged at TIME = 0.008
Network not converged at TIME = 0.009
Network not converged at TIME = 0.01
Network not converged at TIME = 0.011
Network not converged at TIME = 0.012
Network not converged at TIME = 0.013
Network not converged at TIME = 0.014
Network not converged at TIME = 0.015
Network not converged at TIME = 0.016
Network not converged at TIME = 0.017
Network not converged at TIME = 0.018
Network not converged at TIME = 0.019
Network not converged at TIME = 0.02
Network not converged at TIME = 0.021
Network not converged at TIME = 0.022
Network not converged at TIME = 0.023
Network not converged at TIME = 0.024
Network not converged at TIME = 0.025
Network not converged at TIME = 0.026
Network not converged at TIME = 0.027
Network not converged at TIME = 0.028
Network not converged at TIME = 0.029
Network not converged at TIME = 0.03
Network not converged at TIME = 0.031
Network not converged at TIME = 0.032
Network not converged at TIME = 0.033
Network not converged at TIME = 0.034
Network not converged at TIME = 0.035
Network not converged at TIME = 0.036
Network not converged at TIME = 0.037
Network not converged at TIME = 0.038
Network not converged at TIME = 0.039
Network not converged at TIME = 0.04
Network not converged at TIME = 0.041
Network not converged at TIME = 0.042
Network not converged at TIME = 0.043
Network not converged at TIME = 0.044
Network not converged at TIME = 0.045
Network not converged at TIME = 0.046
Network not converged at TIME = 0.047
Network not converged at TIME = 0.048
Network not converged at TIME = 0.049
| 3 | No.3 Revision |
I run a load flow for a case , it converges normally.
When I try STRT and initializing the dynamic simulation , it does not converge as follows:
'' NITIAL CONDITION LOAD FLOW USED 1 ITERATIONS.
| 4 | No.4 Revision |
I run a load flow for a case , it converges normally. When I try STRT and initializing the dynamic simulation , it does not converge .
I got this msg INITIAL CONDITION LOAD FLOW USED 1 ITERATIONS
Then: Network not converged at TIME = -0.002
INITIAL CONDITIONS SUSPECT:
I DSTATE(I) STATE(I) MODEL STATE BUS# X-- NAME --X BASKV ID
2 0.92452E-02 0.53758 GENROU K+1 94000 P.CRUZ 400.00 1
3 0.35834E-01 0.81847 GENROU K+2 94000 P.CRUZ 400.00 1
4 0.16281 0.66431 GENROU K+3 94000 P.CRUZ 400.00 1
8 0.92452E-02 0.53758 GENROU K+1 94000 P.CRUZ 400.00 2
9 0.35834E-01 0.81847 GENROU K+2 94000 P.CRUZ 400.00 2
10 0.16281 0.66431 GENROU K+3 94000 P.CRUZ 400.00 2
14 0.90782E-02 0.52339 GENROU K+1 94000 P.CRUZ 400.00 3
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.