shift factor
Hello, can anyone please tell me how to calculate power flow shift factor in psse?
add a comment
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Shift factor is the difference in flow divided by the load/gen change.
sf = (MW1 - MW2) / (load [or gen] change)
The signs matter as shift factor may be negative or positive.
Example: If you have 100 MW flowing on a line, and you add 1 MW of generation at a particular bus. You now have 100.23 MW flowing on the line, the shift factor is (100.23 - 100) / 1 = 23%.
thank you very much!